Results 1 to 8 of 8
    can anyone help with a question or two please?
    During defrost on a Hussmann case, mod. rca 5lu-do the fans go off during defrost? If they're supposed to, but keep running, what may be the cause?
    thank you.
    Sep 2001
    East Stroudsburg, PA
    Yes, they should, and a bad fan relay or Klixon will cause this.
    Is that the relay at the case, located under the kickplate?
    I'm guessing thats an older glass door freezer case. CARAC?
    if so the fans should turn off during defrost. Go to
    http://www.hussmann.com and click on "products" then "technical info" for impact cases, then go to "reachins" and click on "RL" to get a 6 page pdf. file on similar new cases, it has wiring diagrams for both electric and hot gas defrost, yours should be similar to this. Could be you have a faulty fan relay or if hot gas defrost a faulty fan relay or klixon or the case could be wired wrong.
    Watts New, Ohm My, I been Electrically Commutated. Are U2.
    Apr 2004
    older reachins use kilxons for antisweat and light on one and fan on another with defrost termination on a third. fan relays are used on the newer model cases form the vision and impact line of Hussmann reach in freezers.
    [Edited by smbore on 04-29-2004 at 12:26 AM]
    Orange County CA
    Relay help?
    There's 2 relays in kickplate/raceway.1 is for defrost fans off action. The 208/230v relay coil is powered by def heaters.
    When heaters energized,relay opens fan power.
    The 2nd relay is for fan delay.The 110v coil for this relay is fed through klixon by TXV. I believe this klixon is "close on rise"...I always get RL cases and RCA klixon operation confused.
    Hope this helps
    It looks worse than it is. Good Luck.
    Sep 2001
    Re: Relay help?
    Then what does he need luck for?
    It's Hussmann. It really is as bad as it looks.
    thank you all very much for your help.