    Andover vs. Metasys

    We are in the process of adding a 250,000 sq ft 8 story building. We currently are using JCI web-based system that is N2. I recommended that we go open instead of sticking to N2. Bacnet is the way we are going and the bids started. It came down to Trane, JCI, & Andover. Trane had the highest bid with JCI second and lowest was Andover. I am very happy with the support of our local JCI branch who bends over backwards for us, but in these times it comes down to money instead of people (I'm not a policy maker either). So how does JCI's Bacnet system compare to Andover as far as ease of use and programming. And as far as intergrating the existing Metasys (ADS) system.

  2. #2
    Join Date
    Jun 2001
    Location
    Greeneville, Tennessee
    Posts
    344

    Web base

    How can one get away from the web base??

    I have a customer that is wanting to get away from the JCI web base, as JCI will no longer support the software installed in 2005.

    Java updates are a current problem.

  3. #3
    Join Date
    Mar 2010
    Location
    Georgia
    Posts
    18
    Yeah we have had problems with the Java ourselves. Other buildings that we own use different systems so Java was a constant issue moving between the sites. But, the last update we recieved took care of that problem not sure which update is was though.

  4. #4
    Join Date
    Dec 2006
    Location
    What? Who? Where?
    Posts
    1,703
    Never worked with JCI. But worked as a CxA for a major BioTech firm when they updated their previous generation Andover system (SX-8000/Infinity) to the latest (Continuum) on a 30+ building campus, including office/lab/production/animal/multiple plants all connected together on campus wide grid. BACnet integration/York-Talk integration/Carrier CCN integration. Some intense sequences and tight control. All accomplished by the Andover system.

    It works if the installing contractor know what they are doing. If JCI has been treating you right use them. Who ever gets the project, you should get a independent commissioning authority to verify not only that the installed system is open and meets the owners requirements as documented in the project scope.

    I just completed a project integrating 2 Trane RTU on a MSTP buss into a ALC webCTRL system and there were no issues. Discovered the points, wrote the program, linked the points and it was off to the races. That's the extent of my experience with new generation Trane. I also work on a building that has a complete Trane system (60-70VAV/2 AHU/CH) from 6-8 years ago being brought into WebCTRL via BACnet/IP through the BCU, monitoring only.

    kontrol out
    Last edited by kontrolphreak; 03-12-2010 at 10:50 PM.
    "Open is as open does." - Forrest Gump
    "Can't we all just get a Lon?" - Garry Jack
    "BACnet: integration or interrogation?" - The Janitor
    "Open protocols? You can't handle open protocols!" - Nathan R. Jessup
    “What’s that? Aaa… open protocols? Don’t talk about…. open protocols? Are you kidding me? Open protocols? I just hope we can hardwire an interface!” - Jim Mora http://www.youtube.com/watch?v=U7fjDS0jKiE

  5. #5
    Join Date
    Jul 2007
    Location
    Sacramento, CA
    Posts
    250
    Two things that come to mind,

    First thing is that Andover is part of Schneider/TAC and the software for programming is properitary, unless you get the complete software package with the system.
    JCI Metasys is a little more open in that respect.

    Second thing is that the contractor for the Andover will also try and get into an agreement for service and parts for up to 5 years, but aware.

    Andover is good in that it will integrate most items in the system.

    Make sure your contractor knows what they are getting into with your existing system and not just a saleman pitch for the job.

    Lontshooter

  6. #6
    Join Date
    Mar 2010
    Location
    Georgia
    Posts
    18
    Thanks guys for your input. They are supposed to be giving the complete system for programming and training for five years (service agreements are a dirty word for me so that won't be a issue). I would like to stick with JCI but the decision is not mine to make. The NAE 55's that we have are capable of
    N2 and Bacnet, but more worried about the ADS system that is our archive database and how that would work. I know JCI has a bad wrap sometimes but our local branch is top notch and they know how to treat a customer.