    I have read that you can pressure test a system with CO2, but have always been taught to only use dry nitrogen. Does anyone know of a reason why CO2 cannot be used?

  2. #2
    Join Date
    Mar 2001
    Location
    Halifax, PA
    Posts
    187
    DO NOT use...i repeat DO NOT use co2 to pressurize any refrigeration system. The reason for this is becouse co2 has a high moisture content, which will be very very bad for your system if you add co2 to it. That is why dry nitrogen is used. You will be having moisute problems in the least for the next 100 years......Eric
    If you cant find the time to do it right the first time, then you wont find the time the second time around....

  3. #3
    Senior Tech Guest
    You read wrong...or someone wrote wrong...no co2 for pressure testing period.

  4. #4
    Join Date
    Oct 2001
    Location
    Waterford Michigan
    Posts
    2,668
    We use it all the time no problems.

  5. #5
    Senior Tech Guest
    Originally posted by johnl45
    We use it all the time no problems.
    You mean no problems yet, puts moisture in system, guaranteed.

  6. #6
    Join Date
    Oct 2001
    Location
    Waterford Michigan
    Posts
    2,668
    Originally posted by senior tech
    Originally posted by johnl45
    We use it all the time no problems.
    You mean no problems yet, puts moisture in system, guaranteed.
    No I mean no problems ever on systems that we have service for years!

  7. #7
    Join Date
    Feb 2002
    Location
    Yuma, Arizona
    Posts
    930
    Dry nitrogen is the best and preferred item to put into a system other the refrigerant.
    Now, I did work once with an elder statesman tech that said CO-2 could be used in a pinch. But you do need to take added care. Problems can (and more often do) show up.

    As for absolute NO's in this trade, it keeps changing all the time. Note the thread on mixing some of the gasses.

    But the best to use is a dry product.

    Yuma,
    What is snow? Is it that white stuff in a freezer?

  8. #8
    Join Date
    Feb 2004
    Location
    Midwest
    Posts
    9,937
    I've only done it once but it was on an a/c system, not a refrigeration system. I was trying to open a clogged cap tube, and purged it with dry nitrogen afterwards. That was 20 years ago, and I haven't had the inclination to do it since.

    Conventional wisdom is that, as the others said, the moisture content's too high, but also keep in mind that the pressures are anywhere up to 2,000 psi on a hot day!!! Which brings to mind some problems with what you're going to use to get the CO2 into the system.

    Just blowing out condensers with a refrigerant hose (with the fitting cut off one end), I've had the hose blow a big chewing gum bubble in the middle and pop

    Couldn't hear much for a few minutes.

    Then I got "smart" (NOT!) and flared a piece of 1/4" copper, and it froze to my forearm while blowing out a condenser







  9. #9
    bryan l Guest
    Here is a link to a three page discousion on this topic http://hvac-talk.com/vbb/showthread.php?threadid=35599

    If you scroll down page one and read the third from last on that page there will be a link. The link will show you what is in CO2. The whole topic is a good read.

  10. #10
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,215
    How about pure Oxygen? I hear that's always an exciting leak test...

  11. #11
    acetaline i hear works well to i like smoke while using it just look for the flame and you found your leak

  12. #12
    Join Date
    Jan 2003
    Location
    San Jose, Ca
    Posts
    2,089
    Originally posted by condenseddave
    How about pure Oxygen? I hear that's always an exciting leak test...
    Dave,
    Sometimes you make the hair on the back of my neck stand on edge. When my heart slows down I realise you are just kidding.
    Len
    Old snipes don't die they just loose their steam

  13. #13
    bryan l Guest
    Pure Oxygen. Yah I can just see that now

    WHOMP
    (as all the pictures on the wall for a 5 block radius fall off the wall)

    "Hey John I found that leak we were looking for"

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event