Results 1 to 13 of 24
Thread: Expansion valve issues???
-
03-09-2010, 08:03 PM #1
Regular Guest
- Join Date
- Mar 2010
- Posts
- 8
Expansion valve issues???
I am having issues with a Lennox 410a 7.5ton heatpump system. The system has a dual evap coil ran off a single ciruit compressor. My running pressure are way off with my low side at 60 and my high side at 310. I have checked the lineset for any restrictions and could not find any, I have also checked th expansion valve itself to make sure the orifice was clean. I am not a 100% that my valves are sized properly, there are 2 4ton expansion valves on this coil. Is this correct for a 7.5ton condenser and can a singal circuit compressor handle this dual coil??
-
03-09-2010, 08:14 PM #2
-
03-09-2010, 08:37 PM #3
Regular Guest
- Join Date
- Mar 2010
- Posts
- 8
I opened up my valves thinking there was a screen but found a fixed orifice instead, it was clean of any obstructions. Not sure on the cfm and have not taken any sh or sc readings yet because I am thrown by my pressure's. It seems as though I have a retriction somewhere.
-
03-09-2010, 08:41 PM #4
Member
- Join Date
- Jun 2003
- Location
- Virginia
- Posts
- 376
what was the outdoor temp?? It could be low on charge...
-
03-09-2010, 08:43 PM #5
-
03-09-2010, 08:45 PM #6
-
03-09-2010, 08:51 PM #7
Regular Guest
- Join Date
- Mar 2010
- Posts
- 8
ascj. No the orifice is inside the actual valve. Not sure if that is exactly what it is but it looks like one.
Prorefco. Out door temp was in the low 70's and the charge is not correct I know but when I and refrigerant it just brings up my head pressure.
-
03-09-2010, 08:57 PM #8
Member
- Join Date
- Jun 2003
- Location
- Virginia
- Posts
- 376
Sounds like a restriction alright... Your possibilities are liquid drier, liquid line, metering device (TXV, accurator etc), liquid line service valve, metering device for heating/check valve. What's the temp of the liquid line at the condenser and at the air handler? With a 60 psi suction, you shoud be seeing some frost somewhere....
-
03-09-2010, 08:58 PM #9
Regular Guest
- Join Date
- Mar 2010
- Posts
- 8
ascj. I unscrewed the bottom of the valve where the spring is located and inside where the refrigerant comes in is this Orifice. The best way I can explain it is a small cylinder with 2 small ports at the bottom where the refrigerant comes in and an open end that enters the main valve where the spring is located???
-
03-09-2010, 09:03 PM #10
Regular Guest
- Join Date
- Mar 2010
- Posts
- 8
Proefco. I had just ghanged out the dryer today after seeing my pressure's and the first thing I checked was for some kind of freezing. I could not find anything even at the txv. My line temp pretty much through the system was about 71-72.
-
03-09-2010, 09:04 PM #11
Member
- Join Date
- Jun 2003
- Location
- Virginia
- Posts
- 376
What kind of valve is this? Is it a TXV? (with power element?) What brand? WHat size? Is this a new start-up or an existing system that was working at one time?
-
03-09-2010, 09:10 PM #12
Professional Member
- Join Date
- Jul 2006
- Location
- Anytown USA
- Posts
- 1,952
-
03-09-2010, 09:15 PM #13
Regular Guest
- Join Date
- Mar 2010
- Posts
- 8
Tis is a new start up! The valves were sent out with the equipment.... No power element, and I'm not sure on the brand. I'm really questioning the size on them, there both 4ton valves on this dual coil fed by a 7.5ton condenser.


Reply With Quote