    the airflow back to the return,adjustable

    can you change the air flow goin back to the return,i would like less air goin thru because theres a whistle sound,thanks

  2. #2
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,835
    Post Likes
    Have a Pro add another return, maybe in the master BR,this will reduce the flow at the noisey grilee.

    Second choice, change the grille to a larger one.

  3. #3
    Join Date
    Jul 2007
    Posts
    100
    Post Likes
    Thread Starter
    but,can you change the speed of the air flow to lower or higher to the return,the cfm

  4. #4
    Join Date
    Jan 2010
    Posts
    45,372
    Post Likes
    Better be careful with that and keep it within specs.

  5. #5
    Join Date
    Jul 2007
    Posts
    100
    Post Likes
    Thread Starter
    so it can be done

  6. #6
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,881
    Post Likes
    air flow can be adjusted if it is to high, that is RARELY the case.

    chances are the return is undersized and the best solution is adding more returns or increasing the size you now have.

    undersized return will be noisy when trying to move the proper amount of air and slowing the air down will cause the unit to run to hot or cause freeze up problems for air conditioning.

    undersized return will also hurt overall system efficiency.

  7. #7
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,835
    Post Likes
    Quote Originally Posted by salv97 View Post
    so it can be done
    you can lower the fean speed, which will lower the cfms,but I was assuming it was set correctly. Since it's noisey,the cfms are not likely to be too high now,undersized grille,usually undersized ducts.

    Have it tested and find out.

  8. #8
    Join Date
    Feb 2009
    Location
    Brightion Michigan
    Posts
    31
    Post Likes
    sounds like you might be short of return air.i would have it checked before you start going through blower motors.does the whistle change or stop when you remove the filter?

  9. #9
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by salv97 View Post
    so it can be done
    Yes, it can be done. of course when you do that. It also decreases the amount of air coming out of your supplies.

    Which can cause troubles with your system.

    Better to fix the cause of the noise, then lower air flow.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •