Results 1 to 13 of 16
Thread: Bad Gas Valve
    Jun 2002
    Bemidji, Mn
    Bad Gas Valve
    I am always leary of changing a gas valve out, especially when it requires pulling the fireplace to do so.
    Warnock-Hersey, the thermocouple is on the back of the dang valve so I didnt test mv, but it is enough to hold the pilot. Problem is when the gas valve knob is turned to On (rotated from pilot to on), it drops out. Gen is putting out 400-420 mv disconnected from system, about the same connected...
    I am thinking it has a bad gas valve, or am I missing something here?
    You picked a fine time to leave me loose wheel...
    http://rapalaguy.spaces.live.com/
    May 2005
    Madison, WI
    Warnock-Hersey is a testing agency, not a fireplace mfg.
    If the pilot will hold, it is prob not the valve. I would guess the thermocouple is borderline. I don't think roating the valve knob changes anything that would cause the valve to suddenly close.
    What brand of valve is it?
    Dirty/lazy pilot, is the pilot being pulled away from the thermocouple when main burner ignites? You need to clean it up and get thermocouple readings, I know some of those units can be a pain in the neck to access to install adapter for testing but be patient you'll eventually get it.
    Jun 2002
    Bemidji, Mn
    Quote Originally Posted by blk View Post
    The MAIN BURNER cannot ignite, the pilot instantly drop s out when the valve is turned from PILOT to ON.
    Jun 2002
    Bemidji, Mn
    Quote Originally Posted by jtp10181 View Post
    It says Warnock-Hersey, maybe Im spelling it wrong but thats what it is..
    ... Dont have any model info as I am fairly certain that it isnt pertinent in this scenario? If the thermopile isnt putting off enough mv will it drop out the pilot when its turned to on? Seems odd...
    Warnock-Hersey is a testing agency like Underwriters Laboratories,UL that tests gas appliances. They are not a manufacturer.
    Does this unit have a thermocouple and a thermopile too?
    Common sense is NOT common !!!
    Jun 2002
    Bemidji, Mn
    Quote Originally Posted by logdoc_rob View Post
    Gotchya....
    both, pilot runs off thermocouple and gas valve off thermopile.
    Does the pilot flame drop out instantly when you turn on the main burner, or does it get really small and then within a few seconds goes out completely? If that happens, then there is probably a pressure or volume problem within the gas valve or the gas line leading to the valve.
    If the pilot flame is not hitting the TC properly, you can have very low voltage going to the electromagnet in the safety pilot system within the gas valve. The electromagnet will have enough stregnth to barely hold the pilot valve open, and when you turn the main knob it jars the valve slightly causing it to release. You really need to test the TC voltage.
    Jan 2010
    Are you talking about a thermopile generator ?
    Jun 2002
    Bemidji, Mn
    yes...
    Jan 2010
    Output should probably be between 650-750 mv. Not enough volts to open main valve coil. Can you back off setting to not call for gas when turning on ?
    Jun 2002
    Bemidji, Mn
    I should add this is the pilot control knob that you hold down for the pilot valve to open, it does stay on when the knob isnt depressed...
    Jun 2002
    Bemidji, Mn
    That makes some sense.. or debris coulda jammed into the valve. Customer says all worked fine until one day when the main shutoff was turned off and back on...