    RTHB150 Current overload

    I have a Rthb150 that tripps on current overload only at night on ice making start up. Cts/Compressor mod, all ok per IOMs, just replaced load/unload sol valves as appears pistion press/amp was increasing on a manual hold. Seems to have corrected the problem for a week an reoccured, this problem has been around since start up 10 years agoand has been limited at 80%. Any help or direction would be great( I did attend RTHB training)

  2. #2
    Join Date
    Jan 2010
    Location
    In a Pineapple Under the Sea
    Posts
    149
    Quote Originally Posted by darooo View Post
    just replaced load/unload sol valves as appears pistion press/amp was increasing on a manual hold.
    So the compressor is loading up by itself right?

    Is it fully unloading and amps going all the way down prior to shut down so your'e not getting a loaded start up next time?

  3. #3
    Join Date
    Jul 2005
    Location
    Melbourne Fl
    Posts
    39
    There doenst seem to be a problem during normal run, Only in ice making mode at night, goes into current limit, observed pistion cavity pressure increasing, so suspected load sol valve leaking, did not correct problem. Possibly pistin leaking?

  4. #4
    Join Date
    Jan 2010
    Location
    In a Pineapple Under the Sea
    Posts
    149
    Does the comp cycle at all during the day or once it goes occupied it runs all day? The slide valve pressure should not change by itself, possible internal problems like a lip seal.

  5. #5
    Join Date
    Jul 2005
    Location
    Melbourne Fl
    Posts
    39
    Runs in ice burn mode til about 1000 am then cycles normally, until 400 pm, although there is not much load on the bldg since our temps here in fl have been so low. At 1100 pm goes into ice making mode, starts, loads 100% goes into current limit, as should, seems to try to unload but its like it doesnt fast enough, tripps. I have been able to force it in ice building during the day, to monitor, and same occurace happens. I guess I need to gather some more information.

  6. #6
    Join Date
    Jan 2010
    Location
    In a Pineapple Under the Sea
    Posts
    149
    I think you are not fully unloading at shut down and getting a semi loaded start up. Are you getting any transistion failures too? I think the ice is keeping your load down on the chiller at 10 am and just may be enough to keep it from tripping. At 11 pm your ice is gone and cw temp maybe 15 - 20f warmer putting more load on chiller at start up then.

    Put your gauges on so you can externally operate the slide valve. Put the slide vale in hold, Unload the chiller externaly and see what your amps are. Put slide valve back in auto and let it load up then put the slide valve in unload and see how low your amps go. If everything is working properly your amp readings on both tests should be the same.

    Edit - If you can fully unload it manually do it then shut it down and restart in ice mode

  7. #7
    Join Date
    Jul 2005
    Location
    Melbourne Fl
    Posts
    39
    Thanks I ll try that as soon as possible

  8. #8
    Join Date
    Apr 2004
    Posts
    566
    I would look into inverted starts,compressor taking back liquid,any type of tuning that may alter loading / unloading between comfort cooling and it's ice making pid's,and i would recommend installing amperage recording equip. to pinpoint issue.may not all apply but somethings to ponder.

  9. #9
    Join Date
    Jul 2005
    Location
    Melbourne Fl
    Posts
    39
    Although we have very dirty power here our local utility comp has monitored incoming power, no problems found. Have put on voltage amd current monitors, problem only occurs when starting to full load during the ice making. Since there is not much load right now a full load of ice will last about 3-4 days. I can manually unload to around 40% capasity. But any ideas at this point are of great help. Thanks everyone, its getting old with the 1100 wake up from the summit. Customer is very understanding. (thank goodnesss) but its not 100 degrees yet

  10. #10
    Join Date
    Feb 2006
    Location
    SouthEastern Virginia
    Posts
    1,076
    Is there a Trane factory startup form on site? I would check the original configuration and setpoints against the current setup and see if someone has changed something. You say this has been an issue for 10 years? I'm surprised the customer has allowed this for so long.
    It might get loud!

  11. #11
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,461
    Quote Originally Posted by darooo View Post
    ...At 1100 pm goes into ice making mode, starts, loads 100% goes into current limit, as should, seems to try to unload but its like it doesnt fast enough, tripps...
    how long does this take? 2 hours? 2 minutes? need lots more info...ent/lvg evap AND cond temps. water flows would be nice. first check is whether the settings (like current limit) are correct for this machine.
    How to make the perfect "Half-Hitch" knot or any other boyscout knot in 3 easy steps...

    1. Remove your meter leads from the meter and very carefully return them to their storage case or bag.
    2. Wait 2 seconds
    3. Very carefully remove your meter leads from their storage place and enjoy your new knot!

  12. #12
    Join Date
    Jul 2005
    Location
    Melbourne Fl
    Posts
    39
    I kind of inherited the problam after two previous tech passed away, unit had been set to limit at 80% capasity, all setting are correct. RLA is 313 and set for 313. Trip occurs on start up at 1100 pm I get notified by 1115. Ice usually at 75% full on start up each night, CWT is usaually ambient at time as is a tower on roof. I will be back to log chiller at start up. Thanks

  13. #13
    Join Date
    Nov 2008
    Posts
    366
    Quote Originally Posted by darooo View Post
    I kind of inherited the problam after two previous tech passed away, unit had been set to limit at 80% capasity, all setting are correct. RLA is 313 and set for 313. Trip occurs on start up at 1100 pm I get notified by 1115. Ice usually at 75% full on start up each night, CWT is usaually ambient at time as is a tower on roof. I will be back to log chiller at start up. Thanks
    I am not talking from actual experience on these machines but have heard the recip. guys around the shop talking.

    Does this machine have a CH530 on it and if so do you have the latest version of the software?

    From what I remember hearing the current limit setpoint is ignored in ice making and is at 100% in earlier versions of software, and this was addressed along with some other issues in the loading pertaining to the situation that you describe.

    Like I said this may be wrong as it is second hand but it might jog some of the Trane guys that work on these into remembering something.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event