Results 1 to 9 of 9
    Nov 2009
    Furnace Order of Operations please help
    Well, I couldn't find the "right" section that was public to ask this question so I'm asking here. I'm not 100% on the order of operations in a regular high efficiency furnace, and I was asked the question on an interview, and I'm not sure if I got it right. I know its the most basic question, so if anyone can help me out here, it'll be greatly appreciated. Basically starting at the thermostat call for heat, gas valve energizes ect, I want to make sure I know it and understand it. Thanks in advance.
    Cal
    If you go to a mfg's web site and download a copy of an install manual, the sequence of that unit should be included towards the back, good luck.
    See an attached example
    Virginia
    Quote Originally Posted by hvac_apprentice View Post
    1. Thermostat - calls for heat
    2. Control Board internal/external check (pressure switch open ?)
    3. Inducer motor - ON
    4. Control Board - proves pressure switch is closed, limits and rollout closed
    5. Hot Surface Igniter - ON (warm up timer starts)
    6. Gas Valve - OPEN
    7. Control Board - Proves Flame
    8. Blower timer starts (approx. 45 sec)
    9. Blower - ON
    10. Thermostat - satisfied
    11. Burner - OFF (gas valve closed)
    12. Inducer motor -post purge (time varies)
    13. Blower - OFF(after time delay)
    Last edited by rundawg; 03-01-2010 at 08:26 PM. Reason: added info per bigsky input
    Sep 2006
    Montana
    Quote Originally Posted by rundawg View Post
    6. Gas Valve - OPEN
    9. Blower - ON
    You forgot it has to go through the limits & rollouts before the ignitor glows, part of the safety circuit with the pressure switch.
    Virginia
    Quote Originally Posted by big sky hvac View Post
    I did, thanks.
    Sep 2006
    Montana
    I did, thanks.
    No problem
    Nov 2009
    thank you, that's exactly what I was looking for.
    6. Gas Valve - OPEN
    9. Blower - ON
    Can you do the same thing for a modulate system, or they are the same?
    Virginia
    Quote Originally Posted by 36183 View Post
    Close, but not exactly the same.
    In Modulating Furnaces, the heating mode starts with the gas at 100% and the fan at 0%, the valve reducing and the blower increasing until maximum efficiency is reached. The fan then runs continuously, ramping up or down depending upon air delivery requirements. Since the fan and burner almost never run at full capacity, and energy-robbing on/off cycling is eliminated, the unit is highly fuel-efficient.
    Modulating Furnace Sequence of Operation
    2. Control Board internal/external check (pressure switch open)
    4. Control Board - proves pressure switch closed, limits switches & rollout closed
    5. Servo Valve on Gas Valve is energized-millamp current (NO GAS FLOW)
    6. DSI (Direct Spark Ignition)- Energized
    7. Main Gas Valve Energized (Gas flows at 100% thru warm up period)
    8. Control Board - Proves Flame
    9. Blower - energized (0% RPM)
    10. After warm-up period, the furnace will respond to the thermostat
    demand by altering the gas valve pressure and blower speeds anywhere
    between 40 -100 % capacity.
    11. Thermostat - satisfied
    12. Burner - OFF (gas valve closed)
    13. Inducer motor - post purge (time varies)
    14. Blower - OFF (after time delay)
    Chime in gentlemen if I missed something.