    Does anyone have a copy of the Honeywell form 63-7074 to share that specifies the resistance/temperature association for 20K sensors? I can't seem to find one anywhere on the net and I'd like to reuse some Honeywell T7770 sensors on a LON job.
    Thanks!
    lb
    A hundred million nodes - it's a LON story.
    Jun 2009
    StL, MO
    The TR21 series sensors replaced the T7770s. The TR21s are 20K (except the 21A) and there is a resistance chart in the installation instructions.
    UA LU 562
    www.customer.honeywell.com
    bottom right hand corner...............search
    SoCal
    I have the hokey little Honeywell chart. What I need is a table that specifies specific resistance values over a range of temperatures.
    It seems that the table (form 63-7074) that is referred to in the product literature, has been removed from the planet. Maybe one of you 'old-timers' has a copy?
    Cheers,
    lb
    San Diego, CA
    SoCal
    THANKS DIGO!
    lb
    San Diego, CA
    You're welcome!
    LB, where in SoCal are you at? we're practically neighbors
    SoCal
    Hi Digo,
    We're based in Santa Clarita but service most of the LA area - south from Huntington Beach north up to Bakersfield, east to Pomona and west to Ventura. Most of the work lately is in the
    SFValley and Hollyweird.
    One of my old Elon compadres was also a Brasil-nut - Do you know Howard Herrera? I think he now works for Wattstopper.
    Let me know when you're up this way and I'll buy the cold ones!
    Cheers,
    lb
    San Diego, CA
    Nice. We do mostly SD county, from South Bay up to Temecula.
    We occasionally come up to LA - we have a few buildings we were asked to rescue, hopefully none of yours!
    PM me your #, and I'll call you next time I'm up that way.
    Don't know Herrera, it'd be nice to meet a fellow nut working in this nutty field.
    Jul 2002
    Just some formulas I kepp in my PDA spreadsheet:
    B2 is the temperature cell.
    C7041B,C,D,F,J,K mild temps
    =67993547.1109369*(B2^-1.8919965700969)
    C7170A, C7100A
    =4.8*B2+3114.4
    C7170B,C7100D,C7130B,C7031-PT1000
    =2.1*B2+887
    C7031G2006 w W927
    =-2.2*B2+1914
    C7031G2014 w W927
    =-2.1*B2+3645.7
    C7031D2003,J2009 w W927
    =2.1*B2+935.3
    Jan 2002
    Fort Worth\Dallas, Texas
    If you have an Iphone or Itouch you can get the Temp Chart App and it will break it down in 1 deg incriments for you.
    Go Rangers!
    Sep 2009
    Midwest
    Sep 2010
    Denver, Colorado
    Honeywell 20k Resistance Chart
    This chart worked very well for the Honeywell Series 2000 C7041 20k ohm sensors. Thanks for the link.