Thread: Tracer Gas

  1. #1
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,065

    Tracer Gas

    Does anyone know if you can get bottles of Nitrogen or Helium with EPA approved tracer gas mixed in that can be released into the atmosphere?

    OR

    How much tracer refrigerant can be added to nitrogen and released into the atmosphere and STILL be considered de-minimis.

    Talking about pressurizing racks and there associated loops. At this current time we have an account that is doing large construction and require recovering tracer gas (R-404a).

  2. #2
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,540
    We get calibration gas that is pre-mixed at a specific concentration. That is probably a lot more expensive than you are looking for.

    Never heard of or thought of buying tracer gas for leak detection purposes.

    As I understand it, it is perfectly legal to release the inert gas/trace gas mixture. Your customer is just being difficult.

  3. #3
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,065
    this is what I read on the EPA site.

    "Releases of CFCs or HCFCs that are not used as refrigerants. For instance, mixtures of nitrogen and R-22 that are used as holding charges or as leak test gases may be released."

    To me this reads as. Yes, a mixture of refrigerant and nitrogen may be released.

  4. #4
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,540
    Exactly.

    If customer requires that the charges of 404a be recovered, use a different gas.

    How in the heck are you supposed to recover a gas mixed with nitrogen anyway?

  5. #5
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,065
    how about breaking the vacuum during triple evacuations with 404a?

  6. #6
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,540

  7. #7
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,065
    its what they wanted. they spec not to to break vac's with a non condensable gas.

  8. #8
    Join Date
    Jan 2008
    Location
    michigan
    Posts
    1,145
    Quote Originally Posted by Phase Loss View Post
    this is what I read on the EPA site.

    "Releases of CFCs or HCFCs that are not used as refrigerants. For instance, mixtures of nitrogen and R-22 that are used as holding charges or as leak test gases may be released."
    I've always read this to mean that only r-22 can be used as a tracer gas, and therefore would be no reason to recover r404a since 404 cannot be used as a tracer. What say you?

  9. #9
    Join Date
    Aug 2002
    Location
    Southold.calm
    Posts
    5,535
    Quote Originally Posted by Phase Loss View Post
    this is what I read on the EPA site.

    "Releases of CFCs or HCFCs that are not used as refrigerants. For instance, mixtures of nitrogen and R-22 that are used as holding charges or as leak test gases may be released."

    To me this reads as. Yes, a mixture of refrigerant and nitrogen may be released.
    They use R-22 as an example. You are allowed to use the refrigerant for that system.

    You are allowed to pump the system up to 5 PSIG from 0. The rest of the pressure test or triple evacuation is with N2.

    This also gives you a trace gas for leak detection.

  10. #10
    Join Date
    Aug 2007
    Location
    Winter Haven, FL
    Posts
    4,355
    Quote Originally Posted by monkeyman#1 View Post
    I've always read this to mean that only r-22 can be used as a tracer gas, and therefore would be no reason to recover r404a since 404 cannot be used as a tracer. What say you?
    I say you can use 404 as a tracer. Time for you to buy a new detector.

  11. #11
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,540

  12. #12
    Join Date
    Aug 2007
    Location
    Winter Haven, FL
    Posts
    4,355
    Quote Originally Posted by jpsmith1cm View Post
    I keep a bottle of 'junk gas' and use that rather than waste good gas.

    I have a bottle of mixed refrigerants. Works well for leak detection. Im sure the "purists" are going to preach to me about contamination.

  13. #13
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,540

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event