Results 1 to 7 of 7
    Subcooler testing?
    It might seem pretty simple to test a subcooler, but leave it to me.
    Was looking at one yesterday and trying to test or prove performance. Mostly for my own satisfaction, but also am looking to make this a part of annual testing.
    Inlet liquid temp was 66 degrees.
    Running full subcooling which was a 5 ton valve, I think, at a 40 degree evaporator temp. I measured 2-5 degrees superheat on the subcooler.
    Outlet temp was 67 degrees?
    Something doesn't add up here. What am I missing?
    California
    these reading do not make sense
    First checks are to make sure your subcooling circuit has a solid column of liquid feeding the TEV.
    Then make sure your liquid to be subcooled is a solid column.
    key point here being (you cannot subcool vapor)
    Then your subcooling circuit should have around 10 to 12* superheat (40*SST with a 50* sensible suction pipe temperature)
    Your liquid to be subcooled is entering at 66* and should be leaving towards the liquid header at around 50 to 55* sensible pipe temperature.
    The readings you provide give me the impression that your subcoolers TEV is leaking through the push rods and into the externally equalized line. Giving you a low superheat reading, with no active heat transfer on your liquid to be subcooled.
    Didn't make any sense to me, either, that is why I brought it here.
    Solid column of liquid for both.
    Didn't think about that happening with the TXV.
    California
    Seen it happen a few times.
    If you change the TEV, consider Sporlans Y1155. it is designed for subcooler operation.
    I knew there was a subcooler TEV out there.
    It is a wide range valve, right? That would require repiping to do away with the dual valve arrangement. Might not be a bad thing.
    Apr 2002
    Dallas, TX
    Who else would make a specialized supermarket flow control valve.
    If the only tool you have is a hammer, you tend to see every problem as a nail. Abraham Maslow
    Sounds like you need to set the valve. Why would you remove the duel valve set up? the Y series works well in this application.
    http://www.parker.com/literature/Spo...10/10-10-4.pdf
