Results 1 to 7 of 7
Thread: Subcooler testing?
Hybrid View
-
02-23-2010, 08:23 PM #1
Subcooler testing?
It might seem pretty simple to test a subcooler, but leave it to me.
Was looking at one yesterday and trying to test or prove performance. Mostly for my own satisfaction, but also am looking to make this a part of annual testing.
Inlet liquid temp was 66 degrees.
Running full subcooling which was a 5 ton valve, I think, at a 40 degree evaporator temp. I measured 2-5 degrees superheat on the subcooler.
Outlet temp was 67 degrees?
Something doesn't add up here. What am I missing?
-
02-23-2010, 09:19 PM #2
these reading do not make sense

First checks are to make sure your subcooling circuit has a solid column of liquid feeding the TEV.
Then make sure your liquid to be subcooled is a solid column.
key point here being (you cannot subcool vapor)
Then your subcooling circuit should have around 10 to 12* superheat (40*SST with a 50* sensible suction pipe temperature)
Your liquid to be subcooled is entering at 66* and should be leaving towards the liquid header at around 50 to 55* sensible pipe temperature.
The readings you provide give me the impression that your subcoolers TEV is leaking through the push rods and into the externally equalized line. Giving you a low superheat reading, with no active heat transfer on your liquid to be subcooled.
-
02-23-2010, 09:24 PM #3
-
02-23-2010, 09:39 PM #4
Seen it happen a few times.
If you change the TEV, consider Sporlans Y1155. it is designed for subcooler operation.
-
02-23-2010, 09:42 PM #5
I knew there was a subcooler TEV out there.
It is a wide range valve, right? That would require repiping to do away with the dual valve arrangement. Might not be a bad thing.
-
02-23-2010, 09:59 PM #6The greater danger for most of us lies not in setting our aim too high and falling short; but in setting our aim too low, and achieving our mark. – Michelangelo
There are powers inside of you which, if you could discover and use, would make you everything you ever dreamed or imagined you could become. – Orison Swett Marden
Education is what remains after one has forgotten what one has learned in school. – Albert Einstein
-
02-25-2010, 05:40 AM #7
Professional Member
- Join Date
- Mar 2008
- Posts
- 252
Sounds like you need to set the valve. Why would you remove the duel valve set up? the Y series works well in this application.
http://www.parker.com/literature/Spo...10/10-10-4.pdf