Results 1 to 8 of 8
Thread: 10' deli case question ?
-
02-18-2010, 05:14 PM #1
10' deli case question ?
You know the type: full length gravity coil mounted high, and the same in the bottom section - mounted on the forward wall.
Each case 10; long.
Half glass sloped front for customer display of deli meats with top and bottom sliding worker access doors across the back. Blind storage bottom.
Remote air cooled (cellar rack) condensers.
Big Volume deli - double what an Acme or other typical supermarket does.
Just standard cases - what you've seen in a thousand stores.
You walk into the job fresh - never been there before - what HP woulod you expect the compressors to be?PHM
When faced with the choice between proving that their opinion is correct and changing their mind to fit the evidence - most people get right to work on the proof.
-
02-18-2010, 05:58 PM #2
Do you have the manufacturer and model number?
If not, typically the load will run about 350 Btuh/ft @ +20ºF SST.
I'd say the unit should be a 1/2 HP high temp for a 10 footer.
-
02-18-2010, 05:59 PM #3
1 Hp for 2 units
If you really know how it works, you have an execellent chance of fixin' er up!
Tomorrow is promised to no one...
-
02-18-2010, 06:11 PM #4
Well, I take it all back then
That what is there - 1/2HP compressors. Maybe I'm now losing the Rest of my mind.
Because it sure seems to me that in the last gang of stores we did - the 8' cases all got 3/4HP units. <g>
I'm not doing the cases on this job - just the warehouse and some other odds and ends. But I saw the boxes and condensing units sitting there so I looked. 1/2 HP just seemed light to me.
Guess I'm wrong though. <g>
Thanks.PHM
When faced with the choice between proving that their opinion is correct and changing their mind to fit the evidence - most people get right to work on the proof.
-
02-18-2010, 07:39 PM #5
Piping runs may account for the extra 1/4 hp..
-
02-19-2010, 06:57 AM #6
1/2 HP will do it. You mentioned the condenser was in a rack. How far a run?
--------------------------------------------------------------------------------------
"Give a man a fish he eats for a day. Teach a man to fish he eats for a lifetime"
-
02-19-2010, 09:41 AM #7
No runs yet - the floor is a honeycomb of 8" tubes
The plumber was still digging up the old floor tunnels when I was there. I can only see the tubes from the cellar end. They run out on various angles to all over the store. But the stores ends have all been filled and abandoned. I told them to sawcut the floor to about 3-4" deep under where the cases will be. This cut would have to intersect every buried tube and we all can work with all of them.
But who knows what they will do? When I left they were "projecting" where the ends of the tubes "had to be" and looking for them with a sledge hammer. Like four monkeys and the perverbial football.
Just guesstimating where I think the deli will go as versus where the cellar is - I would guess somewhere between twenty and forty feet of total line run. Call it it fifty feet max - because of the way things go. <g>
Three cases - so IF the floor tunnel is only centered - each of the end cases will have an additional 15-17 feet of run. If they open enough tunnels so that the runs can be on the diagonal - the runs will be shorter.
If things end up like plumbers set them up - the runs will be longer. <g>
PHM
---------
PHM
When faced with the choice between proving that their opinion is correct and changing their mind to fit the evidence - most people get right to work on the proof.
-
02-19-2010, 09:59 AM #8
I have seen a 10' run on a 1/3 hp. I would guess you have a 12' case.
Newer Hussmans require a 1/5 hp for 12' case.Aire Serv of SW Connecticut- Gas heat, dual fuel and central a/c systems installed and serviced


Reply With Quote
