    Wa testing a small RTAC today and noticed after shutdown a tapping noise coming from both discharge lines. Machine is an 03 model...could my check valves be cutting up?


    r404a

  2. #2
    Join Date
    Mar 2007
    Location
    State of Confusion
    Posts
    1,174
    I thought that was normal for the check valves to make noise..lol

    lots of them do it. I don't think anything is wrong..besides its a trane..

  3. #3
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    1,500
    That loud slap you hear after shutdown is the checkvalve(s) closing . Its normal .
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    Whooo Hooo spring at last , time to get the toys out ........vrrrroooooom !!!!

  4. #4
    Join Date
    Oct 2003
    Posts
    1,943
    thanks guys

    trouble is, it was not a single slap, it was a continuos tapping for the remainder of the day. strange


    r404a

  5. #5
    Join Date
    Jul 2009
    Location
    In a mechanical room....
    Posts
    1,879
    Sounds like the stepper motor in the carrier EXV'S sounded like that when they indexed.

  6. #6
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    1,500
    Did you have water flow while it continued to make noise ??? If so it could be that the different temperature of water was causing refrigerant migration making the check valves flutter????
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    Whooo Hooo spring at last , time to get the toys out ........vrrrroooooom !!!!

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •