  1. #27
    Join Date
    Mar 2007
    Location
    tx
    Posts
    1,088
    absolutely! And if I sent one of my guys or I was doing it myself, I would have pulled down the whole lowside. Why???? There was moisture indicated in the system. Why not try to see why. If we pump down the liquid and change the dryer we can't do anything about possible moisture in the high side, but I sure could have made sure it was out of the low and maybe found there was a leak. Also, the filter will catch and hold that moisture until it is saturated, so the sight glass tells us it is not absorbing anymore. We got a lot of moisture in this system. At least get all you can from the low and check for leaks, and give youir new filter a chance at being able to catch and hold the rest. And, just because moisture is caught in the filter, does not mean that moisture has no effect on the system.

  2. #28
    Join Date
    Dec 2004
    Posts
    509
    To answer your question about flow across a solenoid valve;

    Yes they are directional flow valves but if you have a manual stem or you keep the coil energized it will allow flow through the valve. The flow will be restricted but not completely stopped. You can pull a solid vacume acrsos a solenoid valve if it is open.

  3. #29
    Quote Originally Posted by surenuff View Post
    The one thing I have not figured out yet about this site, is why so many people will spend so much time asking questions and waiting for replies to questions that >>>>>by golly they already have all the answers to.
    Because it lead to discussions and you may learn another school of thought. It is HVAC-Talk, after all.

  4. #30
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,665
    Quote Originally Posted by smilies View Post
    Because it lead to discussions and you may learn another school of thought. It is HVAC-Talk, after all.
    Can't learn anything.

    I already know it all.

  5. #31
    Join Date
    Dec 2006
    Posts
    93
    Quote Originally Posted by smilies View Post
    Because it lead to discussions and you may learn another school of thought. It is HVAC-Talk, after all.


    AMEN Prech it Brother!!!

Page 3 of 3 FirstFirst 123

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event