    Carrier Rooftop Ignition Faults

    We monitor and control several Carrier 48TJD008-14 with a DDC system and have noticed several lockouts recently. The heating stage 1 signal has been present for days but the supply air does not rise. Turning off the stage 1 heat signal and then restoring it seems to reset the unit. This seems to be a soft fault that can be reset with out resetting the power.

    We won't reset them in the future so that we can have a tech check for fault codes, but until then. Are there any faults that can be reset in this manner?

    The units were manufactured around Jan 2000, and the ignition control board says Automatic Ignition Systems H33WP002A.

  2. #2
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    18,593
    Yes. When you remove the call, you reset the board.

    A ten year old carrier probably has a bad HX, leading to a rollout switch actuation by flame rollout.

    Other problems typical for the unit include failure of the rollout switch itself, that when it has been actuated a few times, it never fully recovers the ability to close its contacts fully. It is typically not replaced when the HX is replaced, and it should be. The board itself can develop an undifferentiated "internal fault" and it can also show a rollout code when the switch is fine and there is no flame rollout.

    Get your tech out there.

    Get your post count up and apply for pro membership for more specific details in the Pro Technical Forum.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  3. #3
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,720
    Are these zoned systems? Could just be the wind playing tricks on you. Most alarms can be reset in the manner you are doing, if it's something major it's just gonna trip out again. I always like a 3 strikes and your out policy myself.
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  4. #4
    Join Date
    Jan 2009
    Location
    Indiana
    Posts
    3,228
    I thought most roll outs must be manually reset..he is resting in a soft manner.
    i say we cant see from here to judge...it could be a dirty flame sensor or a dirty initiator..wasp nest in draft inducer..etc etc

  5. #5
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    18,593
    Quote Originally Posted by yellowirenut View Post
    I thought most roll outs must be manually reset..he is resting in a soft manner.
    i say we cant see from here to judge...it could be a dirty flame sensor or a dirty initiator..wasp nest in draft inducer..etc etc
    The limit in the blower compartment has a manual reset. The rollout does not.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  6. #6
    Join Date
    Jan 2009
    Location
    Indiana
    Posts
    3,228
    just looked in the manual..u are correct. I still say no one can say with certainty what it is.

  7. #7
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    18,593
    Quote Originally Posted by yellowirenut View Post
    just looked in the manual..u are correct. I still say no one can say with certainty what it is.

    That's right. Only perhaps 90% certainty.








    .
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  8. #8
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    18,593
    Oh, and strangely enough, this is the one design wherein I have never found wasp nests.

    Those little suckers sure do like the Lennox units, though.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  9. #9
    Join Date
    Jan 2009
    Location
    Ontario Canada
    Posts
    33
    The customer's HVAC tech thinks that all faults have to be reset by a hard reset, but our experience shows that some heating faults must be soft resettable. The documentation that comes with the unit doesn't indicate which. I wondered if there may be other documentation you guys may now of. The manual we have is a catalog # 534-725

    Thanks

  10. #10
    Join Date
    Jul 2007
    Location
    Delta BC Canada
    Posts
    91
    It is scary that a fault such as a roll out switch can be reset with out a visual inspection.As was stated before these heat exchangers are famous for rotting out.
    You did not say whether the lock-outs are all on one machine?
    I have even see wasps and flies nest in the regulator vent line (when the screen has rotted out) and cause problems with the heating side.

  11. #11
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    18,593
    Quote Originally Posted by brentstex View Post
    The customer's HVAC tech thinks that all faults have to be reset by a hard reset, but our experience shows that some heating faults must be soft resettable. The documentation that comes with the unit doesn't indicate which. I wondered if there may be other documentation you guys may now of. The manual we have is a catalog # 534-725

    Thanks
    As I said, the rollout switch normally closes when allowed to cool, unless it has been opened too many times, and can no longer close. It must be closed in order for the control board to initiate heat.

    Your tech may be thinking of another brand, one of which I can say definitely must have its rollout switch reset by hand.

    Carrier is not such a brand.

    There are no lockout codes that cannot be reset by removing the call or the unit power. If a code exists because of a hard fault like an open rollout, the fault will lockout the board immediately when the call is made. If, however, the lockout is due to an "internal error," the board may work for a time, and then the code is set once again, and the unit locks out until it is again reset.

    There is a panel in the control section with a label that lists the codes. If rollout is set, check the resistance of the rollout and the HX for holes.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  12. #12
    Join Date
    Jan 2009
    Location
    Ontario Canada
    Posts
    33
    We will check the fault codes the next time it happens.

    Thanks for the replies

  13. #13
    Join Date
    Jan 2009
    Location
    Indiana
    Posts
    3,228
    hmm..i am thinking yes carrier does have the manual reset ones...they are much older units..3-5 ton range. Have that wire that wraps around the burners then back to what looks like a black boob..u press the nipple to reset

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event