Results 1 to 11 of 11
Thread: T991A
    Feb 2005
    Barrie, Ontario
    T991A
    Does anyone know of an electronic or digital version of the T991A Honeywell proportional controller?
    Thanks.
    Is this a Fabreze moment? C.Y.D. I'm voting white elephant. 2.
    May 2009
    northern kentucky
    If you need to stay with the resistance control, Kele makes a good universal resistance transducer model# RES-1E that we use on our boilers to control burner modulation with our BAS. With this you can use any temp. control with a modulating signal.
    Feb 2005
    Barrie, Ontario
    Quote Originally Posted by local 392 View Post
    Thanks for the information. I've been looking it over. It would definitely do the job.
    I have just found the Neptronics KI135 version of it on-line and will get both priced out. I can use either with a Johnson A350PS-1C controller.
    I could replace the old T991A but they are ridiculous expensive for lousy (inaccurate) temp control. Going electronic I hope to get better proportional control.
    It is a simple make-up air and if I can get away without having to replace the actuator I will.
    Jun 2008
    Windsor, Ont.
    Honeywell T775 (modulating) will work with it as long as it's an M91xx series motor your driving.
    http://customer.honeywell.com/techli...0s/63-1318.pdf
    Feb 2005
    Barrie, Ontario
    Quote Originally Posted by nyrb View Post
    Thanks for the answer, but is a M91xx, specifically series 90 proportioning control, the same as a M94xx proportional flame safeguard firing rate motor? I just noted the difference here, Honeywell's page 1...
    http://customer.honeywell.com/techli...0s/63-2691.pdf
    I just can't find enough lit to confirm or deny the T775 will work with the M9484F4001 actuator. I have to prove low fire before the burner motor will start. So that means an upfront r-y (R-W) drive close for the end switch to start the burner motor. By shorting r-y could that damage the T775? I may have to leave compatibility in the hands of our neighbourhood WWG.
    East of big city prices.
    Is it a gas valve your trying to control ? Possibly a V9055? Nevermind I just read where you said actuator. Go to honeywell`s website and email them your question using the contact us feature. They will email you back some correct info. I have done this and the local guy said it would work but Honeywell sent me bulletins saying it would not. Your answer might not come quick.
    Jun 2006
    New Jersey
    Why not use a Honeywell Q7230A to convert the actuator to 2-10vdc. Then you can use that Johnson A350PS-1C. Then to drive low fire you just need to open the circuit, instead of jumping R and W like you were.
    Jun 2008
    Windsor, Ont.
    Quote Originally Posted by gruntly View Post
    Yes the T775 will drive that motor with no issues, it won't drive the old generation of mod motors that are still kicking around on some pretty old equipment. As far as the low fire position goes switch the 'R' wire through a SPDT set of contacts so that R-W(modmotor) is shorted until ignition is completed and then R(controller)-R(modmotor) will release to modulate.
    Feb 2005
    Barrie, Ontario
    Well, thanks for all the replies. Good advice here.
    Looks like it's gonna be a T775M2003 to drive the M9484F4001 firing motor and continue to use the existing low-fire proving relay/end switch because it breaks the "R" controller and closes "R to W" motor until the firing end switch closes, allowing ignition to start, as mentioned above.
    Apparently, I won't need the internal controller switches, hence the M2003, because the existing low-fire proving shouldn't damage or interfere with the new controller (hopefully). The main actuator/valve has it's own POC set-up and doesn't play into the firing/modulating system at all.
    The price is much better for the T775 than a T991 anyway and much easier to install (sensor & controller) in a useful place.
    Thanks for the help. I'll let you know how it goes.
    Jun 2008
    Windsor, Ont.
    Good luck with the job and don't do what I did on my first one and forget the little resistor you need (its included in the package) as per page 8.
    http://customer.honeywell.com/techli...0s/62-0254.pdf
    St Paul, minnesota
    Hmm
    I recently installed a T775M2048 in a direct fired MUA. It replaced a T991 (T991 was replaced 2x in 1 year). this was for a paint booth. the T991 was inside the MUA. If they needed to change the set point they had to go to the roof. it did have a room override which drove the firing rate motor to 100% for paint curing. I installed the T775 next to the summer winter switch, which the customer really appreciated. I had to set the dead band at 20 degrees to keep the valve from hunting. I used sensor "A" for the discharge air and sensor"B" for the room override. works very well.