Air Changes AIA table 7.2
Working on a small remodel job that involves a small procedure room. I need to ventilate the room per AIA Table 7.2 which indicates 12 ACH (air changes per hour).
Wondering if this ACH means the exchange of fresh air/exhaust air? or just 12 ACH of HEPA filtered air?
Thanks
-
02-08-2010, 12:29 PM #2
Professional Member*
- Join Date
- Feb 2010
- Location
- Cal
- Posts
- 1,323
2007 ASHRAE hvac apps handbook specifies for proceedure rooms: positive press, 3 OSA ACPH, 15total ACPH, no air recirc., 30-60 rh, 70-75 f. So does AIA or ASHRAE 62 require more than this? doubtful.