    Carrier 30GH245

    Hello !

    I write for first time in this forum .

    I have wonder if someone can tell me the answer.

    I have a Carrier Air cooled chiller , Model 30GH245
    800 KW cooling power , with 8 reciprocating semi-hermetic compressors 06E. 2 circuits and Refrigerant R22.

    Can this chiller be using for ice rink somehow ?
    The ice rink need about -4 , -5 degrees .

    Thanks in advance !

  2. #2
    Join Date
    Dec 2009
    Location
    Southern US
    Posts
    504
    I believe that unit is only rated to mid to 30's in it normal configuration and I,ve never seen one used for lower than 40 degree supply.

    You need to check with your local reps for a unit designed for low temp apps.
    I'm good at making things cold...You can ask my first two wives!

  3. #3
    Join Date
    Sep 2007
    Location
    Antlers Oklahoma
    Posts
    61
    In addition to this chiller not being designed for this, R22 is not a low enough pressure refrgerant to use in such an application. Not to mention it will soon be a very costly commodity.

  4. #4
    Join Date
    Feb 2010
    Posts
    6

    Carrier 30GH245

    What about if i use ethylene glycol ?

  5. #5
    Join Date
    Feb 2003
    Location
    Wichita Ks
    Posts
    1,467
    I use to have a York system for a ice rink that used R22. It was not a glycol system. The temp was only about 20 degrees. Other glycol systems I have seen had the ice temp of about 25 degrees. Those were ammonia units.

  6. #6
    Join Date
    Dec 2009
    Location
    Southern US
    Posts
    504
    You would HAVE to run glycol since your below freezing!!!!!!!!!!!!!!
    The unit itself is not designed for those temps. Even if the unit has factory options for lower temps they are only down to around mid teens if I'm remembering correctly. Thats not even considering the problems you would have with oil return. There are units that operate on R22 at -15 evap temps but they are designed for those apps.
    I would say the answer to your original question is simply no!
    I'm good at making things cold...You can ask my first two wives!

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event