Results 1 to 7 of 7

Hybrid View

  1. #1
    Join Date
    May 2007
    Location
    Sandyston, NJ
    Posts
    66
    Post Likes

    Trane classroom unit ventilator problem

    I am troubleshooting a DX cool/ Hot water heat system with a ZN510 Board.
    The service call is no heat. The fan runs continously and will not shut off using the built in timer. I can shut the fan off and on using the on/off switch on the stat. I can cycle the unit between occupied and unoccupied mode on the stat. All Functions work when the test button on the board is used. Any ideas. Do I need to access the programing on the board. If so not being an owner of rover software and never using it ,is it worth purchasing. I can from Trane. Does it require training to use.

  2. #2
    Join Date
    Nov 2006
    Location
    New Jersey
    Posts
    78
    Post Likes
    There have been quite a few miswiring issues from the factory on these units. before you purchase rover check the wiring from the timer to the zn. Also sometimes the the wires on the timer contacts have to be switched from N/O to N/C or vise versa. if you turn the timer to on=occupied does the unit turn off? Give about 30 seconds. If it turns off just switch the wires.

  3. #3
    Join Date
    May 2007
    Location
    Sandyston, NJ
    Posts
    66
    Post Likes
    Thread Starter
    Checked today with no results. Any other thoughts. Thanks

  4. #4
    Join Date
    Nov 2006
    Location
    New Jersey
    Posts
    78
    Post Likes
    Now I would suggest purchasing Rover Service Tool or bringing in Trane to check out your problem.

  5. #5
    Join Date
    May 2007
    Location
    Sandyston, NJ
    Posts
    66
    Post Likes
    Thread Starter
    Thanks JD. That seems to be the general consensus.

  6. #6
    Join Date
    Jan 2005
    Location
    NY
    Posts
    73
    Post Likes
    Are you sure its a zn510 and not a zn520. The 520 runs the fan cont when occupied

  7. #7
    Join Date
    May 2007
    Location
    Sandyston, NJ
    Posts
    66
    Post Likes
    Thread Starter
    Its a 520.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.