    New to AX custom programming

    I think im missing something with the "greater than" custom block in the FX60. Where can I set the differential for it? I want to enable an input if the OA-T is greater than 65 degrees but I would also like to but a differential in there.

  2. #2
    Join Date
    Sep 2007
    Posts
    132
    Use the Tstat block
    There's a lot to know.

  3. #3
    Join Date
    Jun 2009
    Location
    StL, MO
    Posts
    580
    You can't. Use the Tstat item in the HVAC section. Note that the differential is centered about the set point.
    UA LU 562

  4. #4
    Join Date
    Sep 2007
    Posts
    132
    Beat you by 1 minute
    There's a lot to know.

  5. #5
    Join Date
    Oct 2009
    Posts
    589
    nice thanks for the help

  6. #6
    Join Date
    Nov 2007
    Location
    Phoenix, AZ
    Posts
    256

    Program

    Quote Originally Posted by Igotworms View Post
    nice thanks for the help
    Igotworms
    You won't find what you are looking for in kitcontol. You have to write one yourself. Email me and I'll send you what you need.