    2.5 ton in place of a 2 ton

    here is one I went out on today. It was not registered and no one told the home owner what the effects would be by increasing the hp size.

    this is the supply duct no transition just blank it off. And lets not put it in the middle where the air flow is.


    This is the 14" return it is .95" wc.


    This is of the inside of the unit you can see the blank off plate covering part of the heat strip.

  2. #2
    Join Date
    Mar 2014
    Location
    Idaho
    Posts
    16
    .95" wc! Next they want a HEPA filter put in....lol you get what you pay for

  3. #3
    Join Date
    Nov 2008
    Location
    Bristol Va.
    Posts
    462
    I failed to mention .95" was only the return.