    Economiser 2-10 vdc signal

    I have a building that is under construction. The engineer has designed a smoke evacuation strategy that requires Carrier economisers to drive full open. I contacted Carrier tech support and they in turn called their engineer who came up with a schematic. This schematic requires closing of a relay that sends 24vac to the 2-10 vdc control input on the damper motor while opening the 2-10 vdc signal. Has anyone seen this done? Will it work without burning up the actuator?

  2. #2
    Join Date
    Oct 2009
    Location
    Nova Scotia, Canada
    Posts
    175
    Post Likes
    I've never heard of sending 24 vac to a vdc motor and it actually driving. Maybe I'm wrong but I'd make sure to have a replacement actuator with you when you try it. Carrier should cover it when it burns up

  3. #3
    Join Date
    Feb 2009
    Location
    Central Oklahoma
    Posts
    26
    Post Likes
    Thread Starter
    Quote Originally Posted by CE-TECH View Post
    I've never heard of sending 24 vac to a vdc motor and it actually driving. Maybe I'm wrong but I'd make sure to have a replacement actuator with you when you try it. Carrier should cover it when it burns up
    That was my initial thought. Have a bunch of spares on hand. But seriously, the actuator is 24vac but normally is driven by a 2-10 vdc signal from the honeywell module based on minimum position, free cooling, co2, etc.

  4. #4
    Join Date
    May 2004
    Location
    Rapid City, SD
    Posts
    7,414
    Post Likes
    If'n it were me (and it's not), I'd probably throw a 24v relay up there and use that, then wire your economizer through the relay.

    I just replaced one of these actuators (if it's the style I'm thinking), looks almost identical to a mod motor for a boiler. The one I put in was 24vac, but it was also driven by 24vac.

    I'm no 'tronic expert, but I've always thought putting DC to an AC device leads to a whole lot of nothing happening. Put AC to a DC device and it might work once, right before it lets the smoke out.
    "If you call that hard work, a koala’s life would look heroic."

  5. #5
    Join Date
    Jun 2006
    Location
    New Jersey
    Posts
    4,456
    Post Likes
    Quote Originally Posted by ltd View Post
    I have a building that is under construction. The engineer has designed a smoke evacuation strategy that requires Carrier economisers to drive full open. I contacted Carrier tech support and they in turn called their engineer who came up with a schematic. This schematic requires closing of a relay that sends 24vac to the 2-10 vdc control input on the damper motor while opening the 2-10 vdc signal. Has anyone seen this done? Will it work without burning up the actuator?
    Hopefully your are understanding the schematic wrong. 24vac to a 10vdc actuator is a quick burn out.

    You don't happen to have a model number of the economizer?

  6. #6
    Join Date
    Feb 2009
    Location
    Central Oklahoma
    Posts
    26
    Post Likes
    Thread Starter
    Thhis is a Carrier Economiser IV, which I looked up on the Honeywell website as a W7212A1017.

  7. #7
    Join Date
    Sep 2007
    Posts
    379
    Post Likes
    That won't work. You can't use an ac signal - the control won't respond. Call again. That is my understanding - let me know if I AM wrong.

  8. #8
    Join Date
    Feb 2009
    Location
    Central Oklahoma
    Posts
    26
    Post Likes
    Thread Starter
    I don't know what kind of electronics are inside this actuator. That's why I am asking the question of whether or not it will drive fully open with a 24vac signal. I wonder if the actuator sees this voltage as a max, sort of like a 10vdc signal. Initially, I thought the engineer was not seeing the same actuator, but then I thought differently.

  9. #9
    Join Date
    Dec 2009
    Location
    Southern US
    Posts
    504
    Post Likes
    Just curious
    Is there a constant 10vdc signal availible?
    If so installing a 24vac relay with 10vdc to N/O would be a quick and simple solution.
    I'm good at making things cold...You can ask my first two wives!

  10. #10
    Join Date
    Feb 2009
    Location
    Central Oklahoma
    Posts
    26
    Post Likes
    Thread Starter
    There is a 2-10 vdc signal available from an AO on the building energy management controls board. That is one option I had considered in conjuncton with a relay, like you said. I thought that would be the easiest option. Until I got the drawing from the engineer, which although it is simple, may not work. So I am asking my fellow professionals for their opinions. Thanks.

  11. #11
    Join Date
    Dec 2009
    Location
    Southern US
    Posts
    504
    Post Likes

    Got to love them engineers!!

    You may want to check with the BAS contractor to be sure your dc signal will be availible if the building goes intomoke alarm. And of course your 24ac would need to be pulled from a source that would also not be shut down.
    Obvious I know but needed to be said.
    I'm good at making things cold...You can ask my first two wives!

  12. #12
    Join Date
    Feb 2009
    Location
    Central Oklahoma
    Posts
    26
    Post Likes
    Thread Starter
    Yeah, those engineers walk on water. Of course, the voltage supplies are all from emergency power, right? If not, more engineers screwed up. I have three methods I came up with to power this damper open during smoke purge. None of them matched the engineers, so I thought he or she might be right and I just didn't understand the inner workings of an HF23BJ054a Carrier actuator made in Germany.

  13. #13
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Quote Originally Posted by can2man View Post
    That won't work. You can't use an ac signal - the control won't respond. Call again. That is my understanding - let me know if I AM wrong.
    I just want to say that you are wrong. Should work I believe it is a belimo motor if I'm not mistaken. What the model number of the rtu?

  14. #14
    Join Date
    Jan 2009
    Location
    Indiana
    Posts
    3,228
    Post Likes
    if the smokies trip that should shut down the supply fans right? then why open the damper? Maybe its just my area but the inspector and fire marshal wants the units dead if they detect smoke....no fans no nothing.

  15. #15
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Quote Originally Posted by yellowirenut View Post
    if the smokies trip that should shut down the supply fans right? then why open the damper? Maybe its just my area but the inspector and fire marshal wants the units dead if they detect smoke....no fans no nothing.
    Smoke evacuation. Supply fans turn off dampers go to 100% and powered exhaust put the building into a negative.

  16. #16
    Join Date
    Jan 2009
    Location
    Indiana
    Posts
    3,228
    Post Likes
    that makes seance to me...but would it pass code? "the doors not locked but i cant open it..grrrr to much pressure." *drinking, forgive my rambelings

  17. #17
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Quote Originally Posted by yellowirenut View Post
    that makes seance to me...but would it pass code? "the doors not locked but i cant open it..grrrr to much pressure." *drinking, forgive my rambelings
    Good point maybe it`s for warehouse or some kind of storage space and not for office space. No fuel no fire right ?

  18. #18
    Join Date
    Oct 2009
    Location
    Nova Scotia, Canada
    Posts
    175
    Post Likes
    What model # unit is it? I know some units have a "smoke evacuation" mode.

  19. #19
    Join Date
    Feb 2009
    Location
    Central Oklahoma
    Posts
    26
    Post Likes
    Thread Starter
    Actually this application is for a county jail. None of the inmates will be leaving. If smoke is detected, return air dampers close, outdoor air damper drives wide open, supply fan runs, smoke exhaust fan energizes, pulling smoke out. The actuator may be a Belimo, it has a Carrier OEM number on it, HF23BJ054A. RTU model number is 48HJE009-551HQ.

  20. #20
    Join Date
    Dec 2008
    Location
    Independence, KY
    Posts
    18
    Post Likes
    Quote Originally Posted by ltd View Post
    I have a building that is under construction. The engineer has designed a smoke evacuation strategy that requires Carrier economisers to drive full open. I contacted Carrier tech support and they in turn called their engineer who came up with a schematic. This schematic requires closing of a relay that sends 24vac to the 2-10 vdc control input on the damper motor while opening the 2-10 vdc signal. Has anyone seen this done? Will it work without burning up the actuator?
    Don't most logic modules have terminals for remote minimum position...? Terminals P and P1 when jumpered will drive full open. Use your relay to jump these two when purge is needed. Won't smoke any motors, but will rely on onboard econ power.

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •