copeland - Page 2
Page 2 of 2 FirstFirst 12
Results 14 to 21 of 21

Thread: copeland

  1. #14
    Join Date
    Aug 2002
    Location
    Orange County CA
    Posts
    1,084
    Originally posted by condenseddave
    Originally posted by oly
    Dice and Bowman, have it, replace the powerhead, I would presume the compressor is cycling on the l/p control. I have not yet seen a txv fail, just the power head..Oh, great this is going to bite me in the @ss....
    There are no bad TXVs, just bad elements and mistaken technicians.

    This doesn't apply in only a few instances, such as TXVs that have permanent power elements.
    Hem057 , if there is nothing for the comp. to pump, how could the head pressure go up. The system probably has more than enough room to park all the refrigerant in the condenser.

    Dave as usual is right on.Powerhead or I bet you gots alot of gummy garbage , or my favorite word for invoicing "debris" in there.

    No bad TXVs just misunderstood.

  2. #15
    Join Date
    Aug 2002
    Posts
    6,047
    Originally posted by condenseddave
    Originally posted by oly
    Dice and Bowman, have it, replace the powerhead, I would presume the compressor is cycling on the l/p control. I have not yet seen a txv fail, just the power head..Oh, great this is going to bite me in the @ss....
    There are no bad TXVs, just bad elements and mistaken technicians.

    This doesn't apply in only a few instances, such as TXVs that have permanent power elements.
    Dave, what about when a tech has turned the adjustment stem so far it has snaped the clip ring? Does not that make the valve no longer workable?

  3. #16
    Join Date
    Feb 2004
    Location
    Medford Oregon
    Posts
    807
    hem075
    a lot of people have given you sugesstions
    what's your status, any response
    what have you found

  4. #17
    Join Date
    Jan 2004
    Location
    Earth
    Posts
    4,879
    R-12 to me that makes the tech no longer workable.

    The Sporlan TXV has got to be one of the most reliable devices in refrigeration. Not perfect but close.
    A Diamond is just a piece of coal, that made good under pressure!

  5. #18
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,215
    Originally posted by R12rules
    Originally posted by condenseddave
    Originally posted by oly
    Dice and Bowman, have it, replace the powerhead, I would presume the compressor is cycling on the l/p control. I have not yet seen a txv fail, just the power head..Oh, great this is going to bite me in the @ss....
    There are no bad TXVs, just bad elements and mistaken technicians.

    This doesn't apply in only a few instances, such as TXVs that have permanent power elements.
    Dave, what about when a tech has turned the adjustment stem so far it has snaped the clip ring? Does not that make the valve no longer workable?
    That would fall under "mistaken technician", or more appropriately, "ignorant gorilla".

    Why? You got something you want to tell us?

    You mean you're not carrying a Sporlan snap ring assortment in your truck???

  6. #19
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,215
    Actually, the bottom cap on the "G" bodies, at least, I believe, are still available as a replacement part.

    Andy might be able to answer that...

    I used to carry a couple spares.






















    BTW. No such assortment, I was busting on you.

  7. #20
    Join Date
    May 2004
    Posts
    28

    copeland compressor with low suction.

    you are bound to find a cpr valve on that hussman that is not openning propely.

  8. #21
    Join Date
    May 2004
    Posts
    28
    if the power element is broken (lost charge) the tx closes off, system will go into a vacuum and stay there. Must still know if a cpr is in the unit. If no cpr troubleshoot metering device, if there is a cpr I bet it is the culprit


Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event