Results 1 to 11 of 11
Thread: Tearing down a compressor
-
03-11-2004, 07:44 PM #1
Regular Guest
- Join Date
- Feb 2004
- Posts
- 126
Any of yall run into this much. Tore down 2 Copeland K body compressors this week. We got slow so I got bored and started tearing them down to see what was wrong. One was 2 years old and the discharge port on the valve plate had blown into many pieces. One piston was coming out of the hole also. It had very black oil in it...may have gotten just a tad warm I think.
The second compressor was about 15-20 years old and I was 110% sure it had a broke rod in it from listening to it. Well it didnt. All the reeds were bent upwards just a itsy bit. Again another one of the pistons on it was coming out the hole. I could put my finger where the piston should have stopped at and it would raise it. Also on this piston you could get a little play in twisting it.
Just curious if its a common finding when tearing one down.
-
03-11-2004, 07:47 PM #2
Professional Member*
- Join Date
- Jan 2004
- Location
- Massachusetts
- Posts
- 650
#1 Sounds like it got hammered with liquid and severe heat
#2 Sounds like it wore out"The value of quality is long rembered after the thrill of low price is forgotten."
-
03-12-2004, 01:56 AM #3
Yeah, they're both common problems with "K" bodies and "E" bodies.
Being air cooled, they're susceptible to damage from excessive heat, and they slug very easily, as opposed to the refrigerant cooled models, which take quite abit more abuse. (The 3D Copelands notwithstanding.
)
I ALWAYS pull the head on an out of warranty K or E before condemning the entire pump. I've found lots of broken valves, replaced them, and sent her off running again. Next to no callbacks after doing this, also.
Just remember to fix the problem, not the compressor. (Find out what caused it, and straighten that out ASAP, and these compressors last forever.)
-
03-12-2004, 08:45 AM #4
Regular Guest
- Join Date
- Mar 2004
- Location
- South
- Posts
- 51
Sounds like they were both slugged. Some "E"s are refrigerant cooled, but all "K's are air cooled. Small compressors are air cooled to avoid the loss in capacity you suffer from heating the return gas before it gets to the cylinder. Also, small suction cooled compressors will run very high discharge temps when running low temp.
As far as piston clearence, don't forget about the valve plate gasket. The piston is machined with a reed relief slot so it can rise slightly above the deck at TDC and fill the re-expansion volume that the gasket would normally create. The reed relief gives the suction reed a place to hide.
-
03-12-2004, 06:33 PM #5
Professional Member
- Join Date
- Feb 2003
- Posts
- 1,165
Seen a lot of these out there with no safties installed. does'nt hurt to install low & high pressure safety's when repairing or replacing.
Watts New, Ohm My, I been Electrically Commutated. Are U2.
-
03-13-2004, 09:08 AM #6
Saftey's. I'll write that down..
-
03-13-2004, 11:11 AM #7
Regular Guest
- Join Date
- Feb 2004
- Posts
- 126
Safeties? You want them installed? Sheesh....most of them are installed but usually dont work or are not adjusted correctly.
Oh and the 2 year old compressor we tore down I have nto seen a reason for slugging. Now the fact the thermostat was turned wide open and never cutting off may have been a factor, thus making the time clock the thermostat. Hoping the thermostat is all it was.
-
03-14-2004, 10:51 AM #8
Regular Guest
- Join Date
- Mar 2004
- Location
- Lombard IL
- Posts
- 171
you would think the protection would be a factory thing?
-
03-14-2004, 05:17 PM #9
Regular Guest
- Join Date
- Feb 2004
- Posts
- 126
Most new Copeland condensing units come with a low pressure switch on it.
-
03-14-2004, 05:50 PM #10
Professional Member
- Join Date
- Feb 2003
- Posts
- 1,165
If I recall right ya dont get them on those Hussmann UML's.
Guess I thought I was looking at Hem's post on the Hussmann unit.
[Edited by mccool on 03-14-2004 at 11:35 PM]Watts New, Ohm My, I been Electrically Commutated. Are U2.
-
05-01-2004, 08:22 PM #11
Professional Member
- Join Date
- Dec 2002
- Location
- davenport, iowa
- Posts
- 777
you might try pulling out the pistons and check the rods; the wrist pin hole is probably wearing out (elongated) which will allow the piston to travel up/down more than normal, i believe the cause is lack of lube from low suction gas velocity,short cycling, liquid refrigerant pulling out too much oil on start up,etc.
Da Threadkilla


Reply With Quote