    carrier 30gxn 090 chiller - Unit is down with no alarms. Setpoint is set at 45* water temp is 78*. Flow switch is closed. When i turn it off then back on exv's close down but unit will not start. In test mode circuit 'A' will come on. But when i test circuit 'B' it will not. Any ideas why this will take place and why the unit won't run. Thanks
    East of big city prices.
    What is the position of the remote- off- enable switch when it doesn't run? And it sounds like maybe circuit B is disabled in the service mode.
    Also another thought did you turn service test off?
    Nov 2009
    switches are in "emergency on" and "enable" . sevice test is off
    Did you check your modes? Check your input for GEN.I , switch and flow.
    Nov 2009
    I havent but i will check in the morning
    Nov 2009
    i did notice that the red light on the MBB board when it blinks, it doesnt go all the way out
    Dec 2006
    phoenix
    This could be a few things but I did a similar problem once. The toggle switch was bad. Once I replaced it, the chiller worked fine. I could run components in TEST mode but nothing would run automatically. I had another 30GX chiller exhibit erratic symptoms the following summer, so I replaced both toggle switches and I've never had a recurring problem with it.
    Good Listener has a good point about checking inputs. Good Luck
    Dec 2009
    Dallas
    You can check under run status to verify switch position. Should show on local when switch is in enable.
    Local 100
    Nov 2009
    it does say on local
    Nov 2009
    Checked configuration. Looked correct.
    Gen.1 stst - strt
    flow - on
    cnd.f - on
    oil.a and b - closed
    opt2 ctrl - switch
    run status - view - stat - on local
    occ - yes
    mode - no overrides in effect
    checked hps and flow switch just to be sure. This unit should be running but it does nothing
    no alarms at all. last one was flow switch.
    Am I missing something? help sure would be appreciated. thanks