    Humidifier model question

    I just had a contrator over to give an estimate for installing a humidifier in my home (suburbs of Denver and very dry). I've done some research including reading many forum posts here.

    House: Built 2003, 2400 sq ft, gas furnace with central air, unfinished basement ~700 sq ft.

    The contractor gave me a quote for an Aprilaire 700. I mentioned that I've read the 600 would be sufficient but he dismissed that outright. I also asked if the 700 would have an outdoor thermometer. He said no because it would also need a controller board and IAQ thermostat.

    Based on what I've read, that doesn't sound right but I'm not an HVAC person (I was an electrician in a previous life). I'd like to hear what you all think and yes I'll be getting a second estimate.

    Thanks,

    Chuck

  2. #2
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Get another contractor. Or educate this one. guess what will be easier.

    The 600 M will do fine for your ize home. Unless you have more then average air leakage into your house.

  3. #3
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    Yea, this one ain't too sharp!

    600 & 700 have similar capacity. We use the 600 if at all possible. Simple, no motors or boards. If you want outdoor sensor capability, get a 600A or 700A.

  4. #4
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by BaldLoonie View Post
    Yea, this one ain't too sharp!

    600 & 700 have similar capacity. We use the 600 if at all possible. Simple, no motors or boards. If you want outdoor sensor capability, get a 600A or 700A.

    LOL. The 600 is only about a ½ pint an hour less then the 700.

    if that ½ pint makes the difference between maintaining the humidity in a 2400 sq ft house or not.
    You have a lot of easy house sealing you can do to make it work.


    Hmmm, That was suppose to be an A in my other post. need more coffee

  5. #5
    Join Date
    Jan 2010
    Location
    Denver CO
    Posts
    5
    Post Likes
    Thread Starter
    Just to be clear, the A means automatic which requires the outdoor temp sensor and has the digital controller? Would there be any reason to get the manual mode in this situation (Denver area with central air)?

    BTW, this is a great HVAC site. It's amazing what I've learned (how bad my HVAC install is) in the last two days.

    Chuck

  6. #6
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    No. With manual. You have to adjust your humidity down as it gets colder out. to prevent condensation on your windows. The automatic. Well, does it for you automatically. You may have to adjust it once. Since some homes windows aren't installed as well as others.

    Yes, A automatic, M manual.

  7. #7
    Join Date
    Jan 2010
    Location
    over here
    Posts
    505
    Post Likes
    All you need is the model 600a humidifier, it has a small outdoor sensor to read the temp so the humidistat which goes on the return air drop can auto adjust the hum to your setpoint. The model 700 is good when the 600 cant be put on the return, so the 700 first recommended placement is the supply. the difference between the output of the two is minimal.

  8. #8
    Join Date
    Jul 2005
    Location
    SE PA
    Posts
    183
    Post Likes
    Curious when the model 700 makes sense, if the capacity is so similar to the 600?

  9. #9
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    When you need every last single CFM of air that the furnace/heat pump can move to be delivered to the house. A bypass can reduce CFM (100 to 150 CFM) delivered to the house.

    When temp rise across the heat exchanger(before you install a humidifier) is providing a discharge temp greater then 130°F.

  10. #10
    Join Date
    Jan 2010
    Location
    Denver CO
    Posts
    5
    Post Likes
    Thread Starter
    One last question on the Aprilaire models. Do they constantly flush water down the drain or only when they are operating? Is it the same for both the 700 and 600?

    Thanks,

    Chuck

  11. #11
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Only when they are running. And its the same for any flow thru humidifier.
    Which both the 600 and 700 are.

  12. #12
    Join Date
    Jan 2010
    Location
    Denver CO
    Posts
    5
    Post Likes
    Thread Starter
    One last question on installation options for the AA600 before the next contractor comes over for an estimate so I don't get lied to again.

    Can the 600 be installed on a return that is only 10" wide or will it have to go on the supply side? I uploaded three pictures. The return is on the left and is 10" wide and 25" deep front to back. I've read supply isn't prefered due to having water above the furnace electronics?

    Thanks again for your advice.

    Chuck

  13. #13
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    The opening that gets cut is all but 10" wide. So it wouldn't mount real well.

    In an absolute pinch. It could be done. But not advisable.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •