    Grounded compressor

    First post here. 6 year installer 1 year tech currently enrolled in a 2 year HVAC program at a West GA Tech. NATE certified ID # 1997427.

    I had a no-heat call the other day on a Lennox HP. The breaker would trip just about as soon as the unit would try to run. Compressor LRA is 85 and read 83amps at startup until of course the breaker tripped. Recip compressor btw and capacitor was in good shape showing proper MFD. Next thought was to check the windings on the compressor. What got me was that each had a reading to ground. Run, start, and common. Diagnosed as grounded compressor heh. But is this common as everyone I seem to have asked has never seen it but it seems totally possible.

  2. #2
    Join Date
    Apr 2008
    Location
    Pluto
    Posts
    983
    No one you work with has ever seen a grounded compressor? Yeah, right. See them all the time.
    Not as lean, not as mean, but I'm still a hardcore, ass-kicking, hard charging Marine! Oohrah!

  3. #3
    Well what i meant was its common to see one winding grounded. What was strange was that all three of them showed a reading to ground.

  4. #4
    Join Date
    Jan 2010
    Location
    over here
    Posts
    458
    Sounds like you answered it.........

  5. #5
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,031
    3 windings?

  6. #6
    Join Date
    Jun 2002
    Location
    Dacula, GA
    Posts
    12,551
    Quote Originally Posted by amasuperbike View Post
    3 windings?

    This thread belongs in the Professional technical forum.
    Last edited by glennac; 01-23-2010 at 12:24 PM.
    "I could have ended the war in a month. I could have made North Vietnam look like a mud puddle."
    "I have little interest in streamlining government or in making it more efficient, for I mean to reduce its size. I do not undertake to promote welfare, for I propose to extend freedom. My aim is not to pass laws, but to repeal them. It is not to inaugurate new programs, but to cancel old ones that do violence to the Constitution."
    Barry Goldwater

  7. #7
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,880
    It can happen.

    Its not actually 3 windings in a single phase compressor.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  8. #8
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,031
    Thats what I wanted him to question and then understand. There is only 2 windings in a single phase compressor. You have to picture that there are two motors in that shell and they are tied together at L1. So its very common to find them grounded at all terminals. Very Common. You will see plenty.

    Shorted compressors are sometimes hard to diagnose with your meter. They throw the breaker as soon as its reset. The best way I have found to be certain its nothing else is disconnect common from the comp terminal without touching anything else. If it resets than it the comp for sure.

  9. #9
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,880
    I think a lot of people get screwed up because a 3 phase has 3 terminals. And they just associate 3 windings with 3 terminal post.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  10. #10
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,031
    Absolutely. Just remember if has a run cap its not three phase. And dont get confused and mistake a fan mtr run cap for the comp.

  11. #11
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    18,260
    ...and remember to


    [edit]

    I just caught myself posting something that could be DIY.

    Get your count up and apply for pro membership.

    See you in the Technical forum.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  12. #12
    Join Date
    Jun 2004
    Location
    Howell, Michigan
    Posts
    16,176
    Moved to Pro

  13. #13
    Join Date
    Jun 2004
    Location
    Howell, Michigan
    Posts
    16,176
    Ok, I moved this to pro and cleaned it up, moved back to residential.

    To the original poster, threads like this are better off in the Professional Forums, get your 15 posts and apply for pro membership.

    Thread closed.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event