Results 1 to 13 of 41
01-22-2010, 09:30 AM #1
- Jan 2010
- 11
Furnace Fan Will Not Stop - Please Help
I was installing a new thermostat. I had to run a 7 conductor wire so that I could have a common. My system is a Amana Distinctions Heat Pump with a gas back-up (aux). When I put the new stat on (Debonair 400) it would not leave the off mode. I could not get it to go to heat or cool. I got concerned so I went to hook the old stat back up. When I removed the new stat, the fan on the furnace kicked on with nothing connected. I immediately hooked up the old stat and it will not shut off. The unit is not responding to the stat. I removed the fan wire at the control panel (G) for the thermostat and the furnace - nothing happened. The unit will not heat or cool either. The only way to stop the furnace is at the breaker (I do not have a switch at the unit).
What could be the problem?
01-22-2010, 09:44 AM #2
Please no DIY posts. See Rules.
You need to have someone look at it. Those T_stats bought at the Hardware stores end up costing you more than you bargained for.
01-22-2010, 11:21 AM #3
- Feb 2009
- God's country
- 36
a mirror could help with this....What could be the problem?
01-22-2010, 11:30 AM #4
Professional Member*
- Jan 2010
- The state of confusion
- 217
You shorted out your system, there will be parts to replace. Have a pro come and repair the damage done, and then have them install a new hoeywell or white-Rodgers T-stat.
The fan running is a safety feature for situations when there is something fried and a short has occured.
Further damage is very likely unless repairs are made by a trained, experienced proffesional.
01-22-2010, 11:31 AM #5
- Jan 2010
- 217
is that ^^^^ OK Stamas?
OKLast edited by Stamas; 01-22-2010 at 07:59 PM. Reason: :)
01-22-2010, 11:42 AM #6
You should have never messed with the stat with the power on the system. Even if we were allowed to give you DIY solutions there is just to much and could get too technical via the internet. Unfortunately the only SOLUTION is to have a professional look at it. They can verify the new stat is compatible and install it for you too. Just make sure you tell them on the phone what you want to be done prior to having them come out, some places dont like using a stat they didnt supply.
01-22-2010, 11:52 AM #7
Banned
- Oct 2003
- Washington
- 7,405
These situations sure are sweet justice
Home Depot, you can mess it up, we can help!Last edited by beenthere; 01-22-2010 at 03:51 PM. Reason: Changed language
01-22-2010, 11:55 AM #8
- Feb 2009
- God's country
- 36
how many of these do you see in a year........
01-22-2010, 12:06 PM #9You sure are cocky for a starving pilgrim.
01-22-2010, 12:17 PM #10
01-22-2010, 12:31 PM #11
- Jan 2010
- 11
Thanks for the repsonses
Thanks for the reponses. I have an HVAC tech out to look at the unit tomorrow. The reason I changed the stat is because the original stat was a HoneywellFocusPro 5000. It seemed like a great stat except you can not change the "deadband" on the stat. If I set the temp to 68 degrees heating mode, it would cycle on and off every 5 minutes. My house never got to 67 degrees. The internal setpoit was like a 1/2degree.
My bills are skyrocketing with the constat starting and stopping of the unit. I am used to the thermostat calling for heat when it drops 2 degrees. There is no setting in this stat to change this. Any thoughts?
01-22-2010, 12:38 PM #12
Have the equipment checked.
What is controlling your dual fuel? That thermostat does not have dual fuel capability. If there is a controller then thats not a problem. Now if you are running the furnace and the heat pump at the same time and the heat pump is shutting off due to high pressure (from the furnace) expect it to have high bills...
01-22-2010, 01:59 PM #13
- Jan 2010
- 11
It is a heat pump thermostat. The reversing valve is wired to the 1st stage of heat(O/B/W1), stage 2 (W2) is the furnace for backup heating.
There is a controller on the outside of the unit that has two relays or transformers on it. There is a condesing unit side, furncae side and thermostat side.