    Confused Unable to Command points in the continuim thru niagara

    Hello all,
    I am trying to be able to change setpoints in a Andover continuim system thru an JACE
    but the actions view is greyed out I have no problems for the honeywell JACE and the JCI JACE but the andover is going thru rs-232 interface and it will not let me change setpoints
    any suggestions??

  2. #2
    Join Date
    Mar 2006
    Posts
    3,639
    Post Likes
    Quote Originally Posted by Dynawiderider View Post
    Hello all,
    I am trying to be able to change setpoints in a Andover continuim system thru an JACE
    but the actions view is greyed out I have no problems for the honeywell JACE and the JCI JACE but the andover is going thru rs-232 interface and it will not let me change setpoints
    any suggestions??
    Are the Jace points "numeric writable" or are they "numeric point"....

    I would bet since the field is greyed out..when you discoved them you did not change them to writable.. Blow one out and rediscover, then use the drop down box to select numeric writable...then add it again.

  3. #3
    Join Date
    May 2008
    Location
    Mid-Atlantic
    Posts
    35
    Post Likes
    Thread Starter
    Thank you Freddy-b
    That turned the trick. Do you know why this one is this way and not the others? I did not have to do this when I discovered any of the other systems points.

  4. #4
    Join Date
    Mar 2006
    Posts
    3,639
    Post Likes
    Quote Originally Posted by Dynawiderider View Post
    Thank you Freddy-b
    That turned the trick. Do you know why this one is this way and not the others? I did not have to do this when I discovered any of the other systems points.
    Bacnet is not that smart.

  5. #5
    Join Date
    Dec 2006
    Location
    What? Who? Where?
    Posts
    2,221
    Post Likes
    freddy,

    Could you please explain how this is a BACnet issue. If the change had to be made in the JACE and nothing changed on the Continuum side would it not be a Tridium issue? Maybe the Niagara is not that smart?

    kontrol out
    "Good" - Jocko
    "Open is as open does." - Forrest Gump
    "Can't we all just get a Lon?" - Garry Jack
    "BACnet: integration or interrogation?" - The Janitor
    "Open protocols? You can't handle open protocols!" - Nathan R. Jessup
    “What’s that? Aaa… open protocols? Don’t talk about…. open protocols? Are you kidding me? Open protocols? I just hope we can hardwire an interface!” - Jim Mora Watch it here!

  6. #6
    Join Date
    Jan 2005
    Location
    NY
    Posts
    9
    Post Likes
    What type of interface are you using to communicate between the JACE and Andover Continuum system? Were you using AX serial driver or BCX router? I have a similar job and was looking to see what options were out there in AX

    Thanks

  7. #7
    Join Date
    Mar 2006
    Posts
    3,639
    Post Likes
    Quote Originally Posted by kontrolphreak View Post
    freddy,

    Could you please explain how this is a BACnet issue. If the change had to be made in the JACE and nothing changed on the Continuum side would it not be a Tridium issue? Maybe the Niagara is not that smart?

    kontrol out
    Might have something to do with no standard....So this AV point might or might not be setup to be writable......so I guess instead of flipping a coin or consulting a medium...they decided to go with the safer of the two.

  8. #8
    Join Date
    May 2008
    Location
    Mid-Atlantic
    Posts
    35
    Post Likes
    Thread Starter
    I am using a AX Serial connection. Works but is VERY slow to update and for that matter slow to do anything! If you have other alternatives try them if the speed is OK. But if you can live with the speed issue then this is fine

  9. #9
    Join Date
    Dec 2013
    Location
    Springfield, MO
    Posts
    10
    Post Likes
    Are you using the Niagara COM1 port to the Continuum COMM1 port (DB9 to RJ45)?