VP525C Series Pneumatic Radiator Valve
installed new VP525C1024 VP525C Series Pneumatic Radiator Valve will not close off steam. i have 10psi at control and at valve actuator. valve had 3-10 psi spring also tryed the 2-5 spring still not closing all the way
what do i need to check now?
-
01-19-2010, 11:44 PM #2
It is a normally open valve so you need full pressure to close it. If it does not close at 15 psi maybe there is a bur on the seat.
http://customer.honeywell.com/techli.../75-5544EF.pdf