Results 1 to 2 of 2
    Nov 2005
    VP525C Series Pneumatic Radiator Valve
    installed new VP525C1024 VP525C Series Pneumatic Radiator Valve will not close off steam. i have 10psi at control and at valve actuator. valve had 3-10 psi spring also tryed the 2-5 spring still not closing all the way
    what do i need to check now?
    Canada
    It is a normally open valve so you need full pressure to close it. If it does not close at 15 psi maybe there is a bur on the seat.
    http://customer.honeywell.com/techli.../75-5544EF.pdf