Results 1 to 2 of 2
    May 2008
    Siebe CP-9302 Valve Controls
    Got a call to fix a Siebe valve. The valve obviously never worked due to the linkage, but on top of that, the wiring is FUBARed. No wire label on the unit. I pulled a diagram from the web, but I'm still scratching my head. The controller is sending the proper 4-20mA signal. Question is which two wires do I land my current on? From the diagram it SEEMS obvious.
    CP-9302 PDF
    http://www.warrencontrols.com/html/pdf/mpprodsht.pdf
    Jun 2009
    StL, MO
    The obvious ones. The installation manual in the following link has lots of footnotes (gotchas). FWIW, we had a pretty high failure rate of these in the early 90s, but the replacements have held up fine.
    http://www.iportalbuildings.com/cont.../F-26563-2.pdf
    UA LU 562