    Carrier to ALC

    I have a couple Carrier chillers daisy chained
    to a Automated logic LGR.
    How can I connect to this LGR to verfiy proper
    communication and if it even reading the points
    correctly?
    Are there proper point tables to refer to?

  2. #2
    Join Date
    Dec 2006
    Location
    What? Who? Where?
    Posts
    1,703
    Are the chillers BACnet? If so which flavour (mstp/arcnet/ethernet/ip)?

    If it is BACnet, once your have made the physical connection to the correct port, you will have to go into WebCTRL disable binding and then discover the chillers, save the points to the DB and then enable the binding. You can then use display blocks in an eik file to display the data. The LGR also supports control blocks for third party devices.

    If it is CCN, I don't know as I have never integrated to a CCN device.

    kontrol out
    Last edited by kontrolphreak; 01-18-2010 at 06:12 PM.
    "Open is as open does." - Forrest Gump
    "Can't we all just get a Lon?" - Garry Jack
    "BACnet: integration or interrogation?" - The Janitor
    "Open protocols? You can't handle open protocols!" - Nathan R. Jessup
    “What’s that? Aaa… open protocols? Don’t talk about…. open protocols? Are you kidding me? Open protocols? I just hope we can hardwire an interface!” - Jim Mora http://www.youtube.com/watch?v=U7fjDS0jKiE

  3. #3
    Join Date
    Mar 2005
    Posts
    168
    Quote Originally Posted by kontrolphreak View Post
    Are the chillers BACnet? If so which flavour (mstp/arcnet/ethernet/ip)?

    If it is BACnet, once your have made the physical connection to the correct port, you will have to go into WebCTRL disable binding and then discover the chillers, save the points to the DB and then enable the binding. You can then use display blocks in an eik file to display the data. The LGR also supports control blocks for third party devices.

    If it is CCN, I don't know as I have never integrated to a CCN device.

    kontrol out

    Its CCN trunk going to a LGR...I need to verify that LGR is setup correctly.

  4. #4
    Join Date
    Dec 2006
    Location
    What? Who? Where?
    Posts
    1,703
    Never done CCN integration. The LGR will have to have a CCN driver installed. You can do a ModStat on the LGR, if the driver is ####-vanilla-### it is only BACnet.

    Checking on the ALC site I see 2 drivers - Carrier DataPort I and Carrier DataPort II. As stated I haven't used these and don't know what they do. I don't have any literature with me but they appear to be for ALC Portals and not LGR. I don't see anything under the LGR driver page for Carrier.

    ****Carrier owns ALC and it appears no talky! *** EDIT: THIS IS INCORRECT IT APPEARS TO BE SUPPORTED NOW


    I'll look into it more when I get back to work next week.

    kontrol out
    Last edited by kontrolphreak; 01-19-2010 at 04:34 AM. Reason: Correcting misinformation.
    "Open is as open does." - Forrest Gump
    "Can't we all just get a Lon?" - Garry Jack
    "BACnet: integration or interrogation?" - The Janitor
    "Open protocols? You can't handle open protocols!" - Nathan R. Jessup
    “What’s that? Aaa… open protocols? Don’t talk about…. open protocols? Are you kidding me? Open protocols? I just hope we can hardwire an interface!” - Jim Mora http://www.youtube.com/watch?v=U7fjDS0jKiE

  5. #5
    Join Date
    Mar 2005
    Posts
    168
    Quote Originally Posted by kontrolphreak View Post
    Never done CCN integration. The LGR will have to have a CCN driver installed. You can do a ModStat on the LGR, if the driver is ####-vanilla-### it is only BACnet.

    Checking on the ALC site I see 2 drivers - Carrier DataPort I and Carrier DataPort II. As stated I haven't used these and don't know what they do. I don't have any literature with me but they appear to be for ALC Portals and not LGR. I don't see anything under the LGR driver page for Carrier.

    Carrier owns ALC and it appears no talky!

    I'll look into it more when I get back to work next week.

    kontrol out


    Thanks!!!

  6. #6
    Join Date
    Apr 2007
    Location
    Amarillo by mornin'
    Posts
    853
    This is from ALC directly. Its what is supported as of 1/10/10
    Attached Images Attached Images  
    "It's not that I'm smart, it's that I stay with the problem longer”
    Albert Einstein

  7. #7
    Join Date
    Dec 2006
    Location
    What? Who? Where?
    Posts
    1,703
    xarralu is correct, they appear to be supported. The third column is for LGR. You will need the driver installed into your LGR. I checked the download page and they were not listed there but the appear to be available via the "find info" search.

    kontrol out
    "Open is as open does." - Forrest Gump
    "Can't we all just get a Lon?" - Garry Jack
    "BACnet: integration or interrogation?" - The Janitor
    "Open protocols? You can't handle open protocols!" - Nathan R. Jessup
    “What’s that? Aaa… open protocols? Don’t talk about…. open protocols? Are you kidding me? Open protocols? I just hope we can hardwire an interface!” - Jim Mora http://www.youtube.com/watch?v=U7fjDS0jKiE

  8. #8
    Join Date
    Mar 2005
    Posts
    168
    How do I check the LGR or modify it
    to make sure it is translating?

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event