Philco Heat Exchanger Rollout
Installed new H/E, now having problem with flame rollout when fire box cover is installed. Run without cover and flame dose not rollout but looks yellow. Removed intake pipe from furnace and still have problem. Please Help! Thank you.
-
01-19-2010, 08:13 AM #2
Regular Guest
- Join Date
- Jan 2010
- Posts
- 6
Looking for suggestions. Have checked: Venting, Gas pressures, Orfices, Replaced inducer blower assembly and gasket, Replaced limit at firebox, Spoke with nordyne tech.
Last edited by kkheating; 01-19-2010 at 10:34 AM. Reason: More Detail
-
01-19-2010, 10:06 AM #3
Since none of us really know what "checked everything" is.
And you didn't post any readings. We can't even begin to help.
-
01-19-2010, 07:10 PM #4
Regular Guest
- Join Date
- Dec 2006
- Posts
- 82
Damn! I have a 1941 Radio made by Philco, and a beautiful piece of work it is... Is this what they make nowadays???
Sorry for OT....
-
01-19-2010, 07:40 PM #5
How is that seal at the top of the hx and the top plate? Burners sitting at the top of the furnace don't like air leakage from the blower.
-
01-20-2010, 10:56 AM #6
Regular Guest
- Join Date
- Jan 2010
- Posts
- 6
Thanks for the help, Im going to the house today and will check seal and then post readings.
-
01-20-2010, 11:12 PM #7
Member
- Join Date
- Nov 2009
- Location
- Lexington,Ky
- Posts
- 23
sounds like your combustion is plugged
-
01-21-2010, 10:06 AM #8
Regular Guest
- Join Date
- Jan 2010
- Posts
- 6
Philco M/N G6RC120C20C
LP Gas pressure @ 10.25"
Firebox sealed, cleaned burners, checked & sealed ID blower, inducer pulling 2"wc at burner box and 2.5"wc at collector box. Orfices in are #54 tech says should be #55, could this be a problem?
Furnace still having flame between burners increases and touches inside of burner box when fire box cover is on, when removed operates rich but flames are proper size.
What next?
-
01-21-2010, 02:30 PM #9
You need a better tech/installer.
Have your tech cal factory tech support, and perhaps get a factory rep out.
The installing contractor can have this done without much trouble or delay.
-
01-21-2010, 03:02 PM #10
Regular Guest
- Join Date
- Jan 2010
- Posts
- 6
Thanks for your lack of advice...Been there done that...meaning spoke to a factory rep and they basically walked away. We did not install the unit but only trying to correct the issues. We'r only looking for a little advice, sometimes a new opinion can help.
-
01-21-2010, 03:05 PM #11
Then call and arrange for the tech rep to come out.
Sorry, this is not a DIY site. So we are not allowed to give out advise of this nature.
Since answering your question in the open Residential Forums would be posting instruction for DIYers that may read this post later.
If your in the trade, get your post count up to 15, and apply for Pro Membership.
Use this link Apply for Pro Membership
Once accepted, you have access to the pro tech forums. Where you can ask and get answers to technical questions.
Plus, you also have access to the Pro Educational Forums.
All of it is free.
Thank you, for your cooperation.
-
01-21-2010, 08:38 PM #12
Professional Member
- Join Date
- Oct 2003
- Location
- Valdosta Ga
- Posts
- 847
warf rat nest in vent pipe