    start cap bleed resistors

    I,ve got two rural locations [bible camps actually]w/w.i.coolers,freezers,r.i.beverage coolers and other smaller refrig.equipment.I know the power is not great because of wind storms causing spikes/whathaveyou.At the one location this spring I installed metal oxide varistors on individual equip.and seams to be protecting compressor electrics where before they would fry in a storm.Owner declined to do anything more costly and utility co.won,t help either.
    At the other place start capacitors want to die frequently[measured voltages are good while there]I,ve read Copeland literature that says they want to see replacement start caps installed w/15-18kohm bleed resistors esp.if equipment is subject to short cycling due to a cple.of things.Question is :jobber start caps a lot of times don,t c/w.Should I be soldering them in?The relays are sometimes failed.Is this because start cap is discharging yet as unit starts again?

  2. #2
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,091
    Post Likes
    :tha,t is the -Purpose o f the Resis,tor's.

  3. #3
    Join Date
    Mar 2003
    Location
    Cochrane, AB
    Posts
    708
    Post Likes
    Quote Originally Posted by dfelt View Post
    I,ve got two rural locations [bible camps actually]w/w.i.coolers,freezers,r.i.beverage coolers and other smaller refrig.equipment.I know the power is not great because of wind storms causing spikes/whathaveyou.At the one location this spring I installed metal oxide varistors on individual equip.and seams to be protecting compressor electrics where before they would fry in a storm.Owner declined to do anything more costly and utility co.won,t help either.
    At the other place start capacitors want to die frequently[measured voltages are good while there]I,ve read Copeland literature that says they want to see replacement start caps installed w/15-18kohm bleed resistors esp.if equipment is subject to short cycling due to a cple.of things.Question is :jobber start caps a lot of times don,t c/w.Should I be soldering them in?The relays are sometimes failed.Is this because start cap is discharging yet as unit starts again?
    You can use crimp connectors to hold the resistors, and yes they are there to protect the start relay from arcing.

  4. #4
    Join Date
    Feb 2004
    Location
    Medford Oregon
    Posts
    807
    Post Likes
    a potential relay is normally closed, if on shut down, any voltage is in the start cap, it will discharge across the relay points, eventually burning them out. That's why they are REQUIRED by Copeland and Tecumseh on any compressor using a potential relay!.

  5. #5
    Join Date
    Jul 2009
    Location
    In a mechanical room....
    Posts
    1,908
    Post Likes
    Do you know how many hits Metal oxide varistor's are good for? One good hit and they are done they work but it's a one time deal.

  6. #6
    Join Date
    Mar 2001
    Location
    Ilwaco, Washington
    Posts
    1,638
    Post Likes
    Get a baggie of 10 @ Johnstone with the terminals already on em G32-082
    One way to outthink people is to make them think you think. They'll think you're not really thinking what you're trying to get them to think you think...........

  7. #7
    Join Date
    Oct 2008
    Location
    OFFICES IN : ARIZONA - NEVADA - TEXAS
    Posts
    258
    Post Likes
    An aftermarket adjustable potential relay would work great for your problem.

  8. #8
    Join Date
    Jul 2004
    Location
    New Jersey
    Posts
    2,911
    Post Likes
    I always install start capacitors with resistors. I don't solder them, don't even need to use spade connectors (have done that too); just put the leads through the holes on the capacitor terminals and twist them nicely with your needlenose. It will do the job.

  9. #9
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    I always thought the resistors were to minimize the arc when the contacts open the start winding.

  10. #10
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,091
    Post Likes
    its to eliminate the arc when the relay resets to its N.C position.

    The resistor bleeds start cap charge so it will not discharge through the start winding when the compressor comes to a stop. If this is allowed to happen, the contacts will arc. And in time..will weld closed.

  11. #11
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    So its not to bleed the charge during the off cycle?

  12. #12
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,091
    Post Likes
    nope, its to bleed the charge during the on cycle.

  13. #13
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    Refrigeration & Air Conditioning Technology 5th Edition must have it wrong read Unit 20.11

  14. #14
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,091
    Post Likes
    yup, sure enough. Page 375 in red ink under safety precaution.

    But look at a wiring diagram and think about how a potential relay works AND you will understand that book is wrong.

  15. #15
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    The book would be correct if it were a current relay and not a potential relay.

    The current relay contacts are normally open, so you would get the capacitor discharging on shutdown, or during the off-cycle.

    A potential relay's contacts are normally closed, so the arcing would occur when the contacts open on startup, or during the on-cycle.

  16. #16
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    Icemeister is my #9 post wrong ( open the start winding or open on startup as you say ) ?

  17. #17
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    Phase Loss i was refering to off-cycle of the relay. My bad because most techs think in terms of compressor cycle. Is off-cycle of the relay even right. Now that i'm thinking about it that should be on not off because when the points are open the relay is on due to EMF or is it CEMF ? Now my head is spinning thanks guys !
    P.S. Did i answer my own post # 11 ?

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •