Results 1 to 13 of 31
    Western Wa
    Confused homemade 4-20 mA/0-10VDC source
    Has anybody out there ever built a homemade 4-20mA/0-10VDC source with two 9V batteries, a 5K pot, and a 500 ohm resistor? The pot and resistor would be 5W.
    Or maybe I shoud use three batterys?
    God Bless the USA
    Jun 2009
    StL, MO
    Sure. Two batteries will be fine unless you plan on 4-20mA through a 1000 ohm load. The following version has a few more components that extend battery life and limit maximum current and voltage.
    UA LU 562
    Aug 2009
    What is the intended purpose of this source? Do you intend to use it as a permanent input to a device or do you want to use it to test things on a bench or in the field?
    Nov 2008
    The next step up is to use a 12v lantern battery 'cause 20 mA from a 9v battery is a little high.
    For 50 cents more, op amps would really be a step up. Their output voltage won't change with varying loads.
    What is the minimum/maximum load resistance you reasonably want to drive? How much current is necessary at 10 vdc? Will 5% accuracy be enough? You want the thing to have it's own meters? What temp. range must the thing work in? How fast must the current/voltage change?
    In my service van checking my lotto ticket
    Quote Originally Posted by WhoIsThat? View Post
    What do you mean by op amps?
    "If you can't explain it simply, you don't understand it well enough”
    Albert Einstein
    "Don't you just love when the flames burn off the wiring schematic?" hvacvegas-HTALK member
    SoCal
    Operational Amplifier
    I assume that is what he is referring to.
    SoCal
    I like to tinker but
    you can buy a Analog Signal Generator (ASG) from Kele for a couple hundred bucks. The Evile Empire sells a nice one for about twice that.
    Nov 2008
    Operational amplifier it is
    http://www.national.com/mpf/LM/LM324.html#Overview
    These things are dirt cheap nowadays.
    And these
    http://www.datasheetcatalog.org/data...wn/mXqxxqx.pdf
    Do you want to run your source off house current or only batteries?
    Sep 2009
    Midwest
    If you are calibrating and need precision, go with Fluke 705 Loop Calibrator.
    http://us.fluke.com/usen/Products/Fl...(FlukeProducts)
    Nov 2008
    Quote Originally Posted by 24vac View Post
    From this link it seems your circuit battery should be at least 28vdc.
    If this thing is $600 and you spend a morning making your own from $10 in parts, you've paid yourself. . .let's see. . .per hour. . .hmmm. . .
    Western Wa
    Just a bench test or field calibration source. For setting up 4-20mA and 0-10, or 2-10VDC stuff. Any ideas or op-amp circuits would be great. Not sure if I want to go AC power or not, but that wouldn't be a bad idea. I would just use my other meters to measure with.
    Thanks to all.
    God Bless the USA
    Nov 2008
    Quote Originally Posted by Randy S. View Post
    Thanks to all.
    If you just need the endpoints, 4.00 mA and 20.00 mA and 0v and 10.00v, it's easier. Would you also need midpoints [12.00 mA and 5.00 v]?
    You want to go that way?
    Apr 2004
    http://www.johnsoncontrols.com/publi.../sysa350p.html
    buy one of these off e-bay the work well as a simulator just replace the temp sensor with a fixed resistor (500 or 1000 i belive)