Thread: Distech ECP-203 Output Question

  1. #1
    Join Date
    Mar 2009
    Location
    Trenton, NJ
    Posts
    5
    Post Likes

    Distech ECP-203 Output Question

    I am having trouble getting a Distech ECP-203 GFX controller online. This is the first Distech programmable controller I have installed so I am not sure if I am doing something wrong. I have written a simple program to control a baseboard heater based on room temp. The program debugs perfectly and when calling for heat illuminates the output status LED on the controller itself. However, I am not getting any voltage from these outputs to close the relay. I checked the configuration of the hardware output, and the output is configured as "digital". I have used Circon, Echelon, and Viconics products before and never had an issue. What am I doing wrong here? Any ideas?

  2. #2
    Join Date
    Dec 2006
    Location
    What? Who? Where?
    Posts
    2,634
    Post Likes
    I have not personally used the controller you mentioned, but the first thing I would check is if the output is a "dry" contact, if so you will have to wire control voltage through the output.

    kontrol out

    For post 308 I give you:

    http://www.gaprecision.net/

    kontrol out again
    "Good" - Jocko
    "Open is as open does." - Forrest Gump
    "Can't we all just get a Lon?" - Garry Jack
    "BACnet: integration or interrogation?" - The Janitor
    "Interoperability? You can't handle interoperability!" - Nathan R. Jessup
    “What’s that? Aaa… open protocols? Don’t talk about…. open protocols? Are you kidding me? Open protocols? I just hope we can hardwire an interface!” - Jim Mora Watch it here!

  3. #3
    Join Date
    Mar 2008
    Location
    NW Ohio
    Posts
    949
    Post Likes
    Quote Originally Posted by Praetorian View Post
    I am having trouble getting a Distech ECP-203 GFX controller online. This is the first Distech programmable controller I have installed so I am not sure if I am doing something wrong. I have written a simple program to control a baseboard heater based on room temp. The program debugs perfectly and when calling for heat illuminates the output status LED on the controller itself. However, I am not getting any voltage from these outputs to close the relay. I checked the configuration of the hardware output, and the output is configured as "digital". I have used Circon, Echelon, and Viconics products before and never had an issue. What am I doing wrong here? Any ideas?
    Which output are you using?

  4. #4
    Join Date
    Aug 2006
    Location
    New England
    Posts
    522
    Post Likes
    The triacs are not internally powered. You need to jump the 24VAC supply to the common of the output (or use a different 24V source). It allows you to use multiple transformers without dealing with isolation relays.

  5. #5
    Join Date
    Mar 2007
    Location
    Netherlands
    Posts
    33
    Post Likes
    Quote Originally Posted by Praetorian View Post
    I am having trouble getting a Distech ECP-203 GFX controller online. This is the first Distech programmable controller I have installed so I am not sure if I am doing something wrong. I have written a simple program to control a baseboard heater based on room temp. The program debugs perfectly and when calling for heat illuminates the output status LED on the controller itself. However, I am not getting any voltage from these outputs to close the relay. I checked the configuration of the hardware output, and the output is configured as "digital". I have used Circon, Echelon, and Viconics products before and never had an issue. What am I doing wrong here? Any ideas?
    Put 24VAC on C1 and connect a wire from DO1 to the coil of your relay if you use output 6 to 8 you must use a 12VDC relay

  6. #6
    Join Date
    Mar 2007
    Posts
    158
    Post Likes
    The Distech triacs are rated for 1A only. Typical you should only drive a 24VAC relay only. Don't be tempted to use the same 24V that powers the node. It's better to use a separate transformer. Also note that you need a load (relay) attached to a triac in order to read voltage. You won't read anything without some kind of load.

  7. #7
    Join Date
    Mar 2009
    Location
    Trenton, NJ
    Posts
    5
    Post Likes
    Thread Starter
    Duh ... yea. Note to self: Remember to check to see if the outputs are triac outputs or universal outputs. Thanks guys.

  8. #8
    Join Date
    Sep 2006
    Location
    EU
    Posts
    171
    Post Likes
    Quote Originally Posted by eyeLON View Post
    It's better to use a separate transformer.
    Why?

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Tags for this Thread

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •