Distech ECP-203 Output Question
I am having trouble getting a Distech ECP-203 GFX controller online. This is the first Distech programmable controller I have installed so I am not sure if I am doing something wrong. I have written a simple program to control a baseboard heater based on room temp. The program debugs perfectly and when calling for heat illuminates the output status LED on the controller itself. However, I am not getting any voltage from these outputs to close the relay. I checked the configuration of the hardware output, and the output is configured as "digital". I have used Circon, Echelon, and Viconics products before and never had an issue. What am I doing wrong here? Any ideas?
-
01-14-2010, 04:49 PM #2
I have not personally used the controller you mentioned, but the first thing I would check is if the output is a "dry" contact, if so you will have to wire control voltage through the output.
kontrol out
For post 308 I give you:
http://www.gaprecision.net/
kontrol out again"Can't we all just get a Lon?" - Garry Jack
"BACnet: integration or interrogation?" - The Janitor
"Open protocols? You can't handle open protocols!" - Nathan R. Jessup
“What’s that? Aaa… open protocols? Don’t talk about…. open protocols? Are you kidding me? Open protocols? I just hope we can hardwire an interface!” - Jim Mora http://www.youtube.com/watch?v=U7fjDS0jKiE
-
01-14-2010, 04:57 PM #3
Professional Member
- Join Date
- Aug 2006
- Location
- New England
- Posts
- 517
The triacs are not internally powered. You need to jump the 24VAC supply to the common of the output (or use a different 24V source). It allows you to use multiple transformers without dealing with isolation relays.
-
01-14-2010, 04:55 PM #4
-
01-14-2010, 06:26 PM #5
Regular Guest
- Join Date
- Mar 2007
- Location
- Netherlands
- Posts
- 29
-
01-14-2010, 06:58 PM #6
The Distech triacs are rated for 1A only. Typical you should only drive a 24VAC relay only. Don't be tempted to use the same 24V that powers the node. It's better to use a separate transformer. Also note that you need a load (relay) attached to a triac in order to read voltage. You won't read anything without some kind of load.
-
02-01-2010, 02:47 PM #7
Professional Member
- Join Date
- Sep 2006
- Location
- EU
- Posts
- 161
-
02-01-2010, 08:48 AM #8
New Guest
- Join Date
- Mar 2009
- Location
- Trenton, NJ
- Posts
- 5
Duh ... yea. Note to self: Remember to check to see if the outputs are triac outputs or universal outputs. Thanks guys.