    Jun 2009
    how to run partial load on carrier 19XR
    Hi all,
    My site is using 2 separate water chillers which the model is 19XRXXXX. my question is will these chillers can be run under its 50% of load? if so, how ?
    I would appreciate all of your quick answer.
    chrin
    Feb 2007
    Baltimore MD ( Balimer, Murilyn)
    Sure these chillers can be run under 50% load, but if you have two chillers running at below 50% load, why wouldn't you just run one chiller(assuming they're on the same chilled water loop)? It would be cheaper energy wise to run one chiller if it is capable of handling the load. Are they in series or parallel piped?
    Southold, NY
    Depending on the exact modes and serial #. You need to contact Carrier for the minimum load on these units. Much below 50% on my 19XRs and theres oil return issues along with Cycle Restarts.
    Dec 2009
    Confused Running at less than 50% load
    Do these chillers have hot gas bypass ?
    Western Wa
    Like any other fixed speed centrifugal, when the vanes are closed that's as small as it gets.
    Then the compressor discharge temp goes up, and the oil return starts having problems.
    God Bless our Veterans
    God Bless the USA
    Jul 2009
    In a mechanical room....
    Quote Originally Posted by Randy S. View Post
    I think he's correct.