Results 1 to 10 of 10
Thread: VMA1420
    VMA1420
    Good-day,
    We have a VMA1420 that is setup for cooling only. This worked fine until modications were done to the AHU which now controls supply air based on OAT.
    Basically, in summer mode the VMA damper will open to cool and close to heat.
    In winter mode, the damper should open to heat and close to cool. But since the VMA is in cooling only, the damper closes when we need to heat up the room.
    Since the VMA doesn't work in this manor (winter mode) how can I change the VMA to open (moduate) the damper in winter to proivde heating.
    In the Q&A no heating is selected.
    Jun 2009
    StL, MO
    HVACpro asks a question (Initiate warmup mode if supply air is much warmer than zone temperature?) that is the answer to yours. If the VMA is not on a network you'll need to add a supply air sensor.
    Another possible option is to configure the VMA with Commercial Zoning Applicatons/Damper Assembly(VMA) in HVACpro.
    UA LU 562
    Mar 2009
    Several Miles from Sane
    Assuming the VMA is pressure Independant you can get it to do what you want...sort of.
    You need to write JCB/GPL so that when the AHU goes into "Heat" you command the VMA first to Unoccupied then to "Warmup", the warm up is a Box Mode function. Make the warm up CFM setpoints about 1/2 of cooling setpoints to start with. The key is in the Supervisory controller logic so you don't over heat the space.
    If sense were so common everyone would have it !
    Any advice provided is worth exactly what you paid for it, not a penny more not, a penny less !!
    NW Ohio
    Try it config'd as CZA.
    Dec 2009
    Canada
    I didn't think the CZA supported pressure independant control. Haven't used it in a while though, so I'm not really sure.
    NW Ohio
    Quote Originally Posted by DreamCar View Post
    Yes, it doesn't..........and?
    Dec 2009
    Canada
    Quote Originally Posted by NINAX View Post
    If my recollection is sound (a big if...) you can't download a pressure dependant sequence into a VMA-1420.
    NW Ohio
    There seems to be a around trend here, more and more "I don't know, but" and "I've never used one, but"....
    Not specifically directed at anyone, just a general observation.
    Dec 2009
    Canada
    Right you are, I should have checked before posting. It was late & I wasn't at my work laptop. Just lazy!
    This is however an open forum for discussion, and I for one would rather know the poster's level of confidance in their answer than assume they're 100% sure.
    NW Ohio
    We're on the same page.