    Here's something new from Copeland for the new year:

    http://www.emersonclimate.com/en-US/...aloverview.pdf

    Plus an interesting video:

    http://www.youtube.com/watch?v=2B7kX8RavcY

  2. #2
    Join Date
    Jun 2001
    Location
    Michigan
    Posts
    12,077
    Post Likes
    I have already seen this in use. It aint perfect

  3. #3
    Join Date
    Jul 2005
    Location
    Southern California
    Posts
    620
    Post Likes
    Quote Originally Posted by Dowadudda View Post
    I have already seen this in use. It aint perfect
    I haven't seen any yet. What issues have you seen?

  4. #4
    Join Date
    Nov 2004
    Posts
    78
    Post Likes
    The ISD controllers can be troublesome. Go off line like a regular cpc board and cause issues..

    when it runs in fail safe the manual high and low safety come into play and they use the non adjustable screw on style which suck..the settings are way to low for 404 med temp causing the rack to run flat out.
    The nice part about the ISD is you can monitor amperage, cycle counts, dis temp, suct temp all together.

  5. #5
    Join Date
    Jun 2001
    Location
    Michigan
    Posts
    12,077
    Post Likes
    pulse width modulation is not ideal pressure control. What they did was used the same thing they are using in the scrolls. And it does not hold tight control. It's choppy.

  6. #6
    Join Date
    Mar 2008
    Location
    Banana Republic,Florida
    Posts
    400
    Post Likes
    i service a tarjay store that has this set-up and its good havent had a single failure
    Mastic its whats for dinner!

  7. #7
    Join Date
    Jun 2001
    Location
    Michigan
    Posts
    12,077
    Post Likes
    maybe you aint lookin hard enough??

  8. #8
    Join Date
    Aug 2002
    Location
    Orange County CA
    Posts
    1,084
    Post Likes
    I'm not a big fan of the Dig. Scrolls...I agree with Dow...too clunky.

    The unloading is time based. Sometime it's hard mellow it out.

    I can't see the Recips being much better... If they could do variable unloading that would be awesome.

  9. #9
    Join Date
    Jun 2001
    Location
    Michigan
    Posts
    12,077
    Post Likes
    Copeland has a hard on for this all because they are trying to go with scrolls in most apps. They wished it was scroll all the way. But they got to deal with the recip market. There is simply too much demand to ever depart from it. So in stead of doing what almost everyone else has done, using drives on recips, they figure if they can run a recip like they do their scrolls, with the same POS control using PULSED WIDTH MODULATION. To understand this all you have to do is understand the PWM is nothing more than 20 second windows. In them 20 seconds, it will be determined by set point how long loaded and unloaded the pump will be in that capacity. It can be very choppy suction. It's okay but don;t expect miracles with it.

    After working with a few drives, and then you go try and tweak one of these digital controllers, it's night and day. The digital control sucks. On a rack with constant load changes the suction can be very choppy. On singles it's worse. Frequency drive is the only way these days. It's getting cheap.

  10. #10
    Join Date
    Nov 2009
    Location
    Richmond, working under tarps
    Posts
    711
    Post Likes
    not very impressive.

    digital=binary..........= on/off..........not effective in capacity control IMHO.

    copeland....outa figure out how to stop annoying oil leaks in the their baseplates first.

  11. #11
    Join Date
    Jun 2001
    Location
    Michigan
    Posts
    12,077
    Post Likes
    Additionally, they have yet to come out with a integrated single control for it. You have to have like a AK255 or an e2 to run it. Let's say you wanted to do this to a single. Like we all talk about on here, where you have a single with multiple loads. You can not deploy this with out something like a rack controller because it needs the analog input and set point reference. A guy can do it with temperature using the digital stats. But I have not seen a contraption that will do analog for pressure.

    I went to a seminar a few months back and this dude was touting this as the next big thing. SO I asked him and informed him of how choppy and how not tight of control it is. He tried hard to shut me up in front of the audience. And I don't even think he or the audience was understanding what I was saying. I don't think they understood choppy. Or how I was trying to explain tight suction.

  12. #12
    Join Date
    Aug 2002
    Location
    Orange County CA
    Posts
    1,084
    Post Likes
    If the cycle window could decrease to 3-5 seconds , it would be so much better. I think now it's a 10-20 second window.( I forget)
    The thing that makes me laugh is that they are bragging about unloading down to 10% ( if I remember)...yeah that's impressive but, That's 100% compresser for 1 second and unloading for 9 sec.( or whatever the window is).

    If it was CFM reduction from (example) 1000 CFM to 100 CFM I'd be impressed. If 100$ bills came out of my dogs behind..I'd be impressed.
    If my credit cards were suddenly payed off...well you get it.



    But at the shorter window the valve would probably die much quicker death(too many cycles)

    A VSD on an E2 is the stuff , if all is dialed in correctly. But you still have low limits for oil issues.

  13. #13
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,090
    Post Likes
    If they wanna save some money in efficiency...they need to buy a damn screw with VSD and be done with it. Stop buying inefficient recips.