    dead zone

    I have a dual fuel hp amana /propane that is set to switch over to propane at 20 degrees It works great except for the fact as the outside temp begins to rise the propane keeps running untill about 27 degrees Is this normal

  2. #2
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    33,907
    What control? A Vision Pro has a 5° deadband so it should rise to 25° before going back to pump.

  3. #3
    Join Date
    Jan 2008
    Posts
    19
    The control is a rotating outdoor themostat my heat pump thermostat does not control the switchover to propane

  4. #4
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,743
    Sounds like the differential is set that high.

    Its a little high then I would set. but, may be just what your installers standard setting is.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #5
    Join Date
    Jan 2008
    Posts
    19
    What dfferential please explain

  6. #6
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,743
    The stat is set to have a temp to switch to aux. And the differential is the amount of temp the outdoor air must rise before it switches back to heat pump.
    Non as either dead band, or differential.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  7. #7
    Join Date
    Aug 2002
    Location
    Southold.calm
    Posts
    5,429
    Dead Band I don’t know. Differential Yes

    DIFFERENTIAL - The difference between the cut-in and cut-out of a control.

  8. #8
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,743
    Quote Originally Posted by pecmsg View Post
    Dead Band I don’t know. Differential Yes

    DIFFERENTIAL - The difference between the cut-in and cut-out of a control.

    Dead band.

    Area (temp range) of no change from previous function/condition.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  9. #9
    Join Date
    Jan 2008
    Posts
    19
    thanks for the explaination. I am curious why does there need to be a differential of several degrees?

  10. #10
    Join Date
    Jun 2006
    Location
    Omaha, Nebraska
    Posts
    861
    The outdoor temp typically fluctuates a few degrees all day long depending on cloud cover, wind direction, etc. With a low deadband (differential) of 1-2degrees the HP might be switching back and forth between gas and mechanical heat frequently when the outdoor temp is right around the setpoint. I would think a deadband of 4 degrees might be a little better. Your outdoor stat might have and adjustable differential or it could be non-adjustable.

  11. #11
    Join Date
    Jan 2008
    Posts
    19
    thanks all