    FX graphics - Point Values

    I am using a point that is either ON or OFF. When the point is ON it is in alarm. I am using a BoundLabel to display the value of the point.

    How can I change the color of the BoundLabel to Red when the point is ON ??
    Last edited by exwtk; 01-10-2010 at 10:55 PM.

  2. #2
    Join Date
    Jun 2009
    Location
    StL, MO
    Posts
    677
    Post Likes
    Here's one way.
    Edit the point, look for the Text item. Click the button to the far right (square with three dots). A little box comes up, change the Format to %out.value%
    Save.
    UA LU 562

  3. #3
    Join Date
    Mar 2007
    Posts
    295
    Post Likes
    Thread Starter
    If I do that then the value reads: %err:baja:Boolean: out%

  4. #4
    Join Date
    Sep 2007
    Posts
    71
    Post Likes
    Open the bound label for editing, right click on the word foreground and select animate. Converter type should be "I Boolean To Simple". Choose colors for true and false values. You can do the same for "blink" if you want it to blink when in alarm too.

  5. #5
    Join Date
    Mar 2007
    Posts
    295
    Post Likes
    Thread Starter
    ah ... so simple once you know how to do it... Thanks foyler