    VisionPro IAQ question: how to tell if Aux heat is on

    Hello, I have a 17seer 2 stage comfortmaker heat pump with 2 stage electric strip auxillary heat. I have the lockout temp set for about 10F (so that I don't damage the compressor) but this morning it was about 5F Outside, the Heat Pump was off, but the thermostat still says "heat". How do I tell what stage of heat the thermostat is using? Is there any way to tell if it is kicking in the auxillary heat at all?

    Thank you!!

  2. #2
    Join Date
    Jul 2008
    Location
    Denver, CO
    Posts
    4,207
    Watch your electric meter, you will know when the electric heat strips kick in.

  3. #3
    Join Date
    Jun 2005
    Location
    Near Chicago, IL
    Posts
    3,316
    I have a dual fuel setup, and mine says "aux heat on" when the furnace kicks in.

  4. #4
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    66,807
    If the outdoor unit isn't running. And its still putting out warm/hot air. the aux must be on.

    PS: Running the heat pump at 0 outdoor temp won't hurt it.
    And will probably save you money on your heating bill.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #5
    Join Date
    Aug 2009
    Location
    East TN
    Posts
    129
    From page 4 of the Operating Manual, the display should read Aux Heat On.

  6. #6
    Join Date
    Dec 2008
    Location
    VA
    Posts
    218
    the visionpro 8000 has a red led in the corner that comes on, im not sure if the iaq has it though

  7. #7
    Join Date
    Jun 2007
    Location
    The Twilight Zone
    Posts
    2,964
    Quote Originally Posted by doinkeroni View Post
    I have the lockout temp set for about 10F (so that I don't damage the compressor)
    If you have electric resistance as auxiliary heat, I wouldn't lock out the compressor.

    You won't hurt the compressor by running it at low temps. The aux electric heat will cycle on/off as needed while the compressor runs continously.

    My 14 SEER 9 HSPF heat pump has a C.O.P of 2.47 at 10F ambient. That means it's 247% cheaper to run than electric resistance heat.

    Take care.

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event