    RTU supply fan sometimes starts and sometimes not. I have a diagnostic
    "OA humidity sensor failure" I replaced the sensor but the diagnostic is still there after resetting. Upon startup the oa damper opens to 10%, unit goes to occupied mode, the K-2 relay on the RTM closes (Enableing the vfd) but no speed signal is coming out of it. After about 2-3 minutes I get "supply fan failure"
    When it does try to start, it tries to ramp up to 60hz but before it gets there it shuts down and I get a "space pressure sensor failure". Does anyone have any ideas?
    Thanks in advance
    Is the pressure sensor it is controlling to ok?
    May 2005
    It seems to be.
    Oct 2007
    Austin Texas
    I've got a couple of I-pacs on my roof that will still run with the diagnostic that you describe.
    Nemo me impune lacessit.
    May 2005
    ok...thanks. Any idea why the supply fan wont start?
    Oct 2007
    Austin Texas
    I would start with the VFD.
    chicago
    Quote Originally Posted by John Culpepper View Post
    I had the same problem last year, unit under warrenty, Trane came out and replaced the vfd. Trane VFD has a tech support # 1-877-872-6363
    Oct 2007
    Southern Indiana
    Check the pressure switch in front of the fan. Its down by the motor mounted on the panel to the right of it. It's the supply fan proving switch I have changed a few of those. If I remember correctly it had the same symptoms you are describing.
    Southeastern Pa
    Quote Originally Posted by GOVHVAC View Post
    During the summer of '08 I found a bad crimp on one of the two wires that connect to the pressure switch. I found it when I placed my hand on the connector and pulled it off the spade terminal and the wire popped out of the end of the connector. It had been crimped onto the insulation, and not the wire conductor.
    I also pulled a panel (with door and hinge assy) to reach it more easily.
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    Nov 2005
    I doubt the supply air dp switch controls the vfd. I have had supply air proving switch failures and it has always been the switch or a dead fan motor. I would suspect that the vfd is the issue and the proving switch is doing its job.
    Space pressure sensor fault? I have not seen that before. Find the space pressure sensor and verify that it is operating correctly.
    I STARTED WITH NOTHING, AND I STILL HAVE MOST OF IT!
    Oregon
    They have service mode for trouble shooting.
    Federal Reserve, stealing your kids futures since 1913
    UA290
    Bend, OR
    Trane I paks supply fan will start with a 0% single to the VFD. A start command will be sent and then the UCM controller looks for a closed pressure switch within 1200- 180 seconds. If no proof made the unit will shut down . There is typically a couple pressure transducers in the fan cabinet. Duct static, Building Static, High Static Safety. Check tubing and terminators for obstructions and breakages. 0-5 vdc signal from transmitters.
    Nov 2009
    Aptos, Ca
    Check the K-42 relay in the vfd compartment for proper operation. Terminal 12 on vfd is 24Vdc out. see that you also have 24vdc at terminal 18 and 27 when you start the unit, these are the interlocks. Terminal 53 is the 0-10 or 2-10Vdc drive speed command. Minimum speed should be 22hz. Also as mentioned below, in the filter access compartment above the economizer motor and exhaust damper motor are the transducers for space pressure and static pressure. Check and make sure the pnuematic tubing is proerly attached and not backwards also check the wiring plugs. Of course run the unit in test mode and then use the status menu to see if you are building supply air static and any measurable building static. Also in the supply air section next to the fan discharge is the supply fan proving switch and the static pressure pick-up cone. I have seen those tubes rub holes in each other. Check the plug on the econo module in the control panel that receives the building static input. Its also possible you have a failed module.