Check the location of the defrost thermostats, some of the units are coming (from Mexico) with the defrost thermostat mounted on the wrong side of the 'T', look in the IOM for the correct location. Also if two stage unit check that defrost thermostat is mounted on correct coil for the reversing valve it is controlling.