  1. #321
    Join Date
    Jan 2008
    Location
    michigan
    Posts
    1,187
    Post Likes
    Quote Originally Posted by fruecrue View Post
    Today's voltage reading was 253.6, up from 246.9. Amp draw was around 14, Power factor was around .38-.44, measured at the contactor load side.

    Recent history in house- bar fridge failure, compressor and circuit board warrantied by manufacturer's rep. Boiler pumps, pool exhaust fan and brand new hydraulic motor for pool cover all whine with a very high pitched harmonic noise. Dryer vent booster motor intermittently fails.

    The PF (as pictured in previous post) was defended by installing electrician to be biased because of close proximity to inductive load(blower motor). He plans to move his data recorder to main service next.

    At this point, I have stepped aside and will let customer and electrician sort out their issues.
    Stebs, this was the data recorder(not mine), I wouldn't mind having access to this thing either.Attachment 69342
    Me thinks Mr. Fruecrue is hands off at this point.

  2. #322
    Join Date
    Sep 2009
    Location
    Arnold mo
    Posts
    3,974
    Post Likes
    I'm thinking if I was wrong about the electricians amp meter not being able to read true current with non-sinusoidal harmonic distortion, then the fact that fruecrue read 12 amps and the electrician read 14 amps could well be an indication that harmonics due to non-linear loads is present. These loads can create a harmonic distortion to the current that is 30 or more % that a non-true rms amp meter can read.

  3. #323
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by monkeyman#1 View Post
    Me thinks Mr. Fruecrue is hands off at this point.
    I was hoping he'd find out when he went back to make that unit work, after whatever gremlins are dealt with.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  4. #324
    Join Date
    Jul 2008
    Posts
    1,589
    Post Likes
    I have not yet googled this yet, I'm sure I can find the answer but for the sake of sharing and since I don't have a lot of time, I'll ask the question out loud. Looking at an old Rheem diagram I noticed a device called a power fcator choke. You can see it on the attached diagram. What I wonder is, what is it and how does it work and would one have helped frucrrue's situation.

    Attachment 70292

  5. #325
    Join Date
    Nov 2008
    Location
    Meriden, Kansas
    Posts
    435
    Post Likes
    Most ECM motors use a "power factor choke" to reduce the effects of harmonics on the true power factor. That's what you see on the diagram. Even though the power factor of an ECM is theoretically 1, the harmonics cause problems that a choke can reduce. Chokes are one of the methods used to control harmonics and might help this situation, but again it needs to be designed or specified for the exact problem existing.

  6. #326
    Join Date
    Jul 2008
    Posts
    1,589
    Post Likes
    Quote Originally Posted by ChuckHVAC View Post
    Most ECM motors use a "power factor choke" to reduce the effects of harmonics on the true power factor. That's what you see on the diagram. Even though the power factor of an ECM is theoretically 1, the harmonics cause problems that a choke can reduce. Chokes are one of the methods used to control harmonics and might help this situation, but again it needs to be designed or specified for the exact problem existing.
    Thanks for that explanation, I actually could not find much on google. Now another question, what harm is being prevented? What would the harmonics do if not prevented/reduced by the choke?

  7. #327
    Join Date
    Sep 2009
    Location
    Arnold mo
    Posts
    3,974
    Post Likes
    Quote Originally Posted by Pneuma View Post
    Thanks for that explanation, I actually could not find much on google. Now another question, what harm is being prevented? What would the harmonics do if not prevented/reduced by the choke?
    Here is one article I found that explains a bit about it. I'll copy a quote out of it along with the article.

    POWER FACTOR & HARMONICS
    The response of the building system to the application of ECM vs. PSC motors is different. There are
    issues of power factor and harmonics that warrant some discussion. Without presenting a discourse on the
    basics of alternating current, there are three issues that need some understanding:
    • Displacement Power Factor: PSC motors have a power factor that is primarily a function of the phase
    angle between line voltage and the line current flowing to the motor. The displacement power factor for
    ECM motors is 1. For PSC motors, it is about 90% at rated load, and can degrade to 60% at off load
    conditions.
    • True Power Factor: The true power factor is the ratio of power consumed (in watts) to the volt-amperes
    needed to supply the load. For PSC motors, the Displacement and True power factors are the same.
    For ECM motors, however, there are harmonic effects that can cause a difference between the two.
    • Harmonic Currents: These are a collection of sine waves whose frequencies are integral multiples of
    the fundamental frequency of a non-linear waveform. These factors are significant in buildings with
    three phase wye-connected distribution systems, and are generally addressed in the power distribution
    design in order to contend with electronic ballasts, computer and other electronic loads.
    The consequence of the differences between ECM and PSC motor applications is that the building
    electrical system must contend with the greater harmonic distortion created by the ECM motors, and that
    technicians should understand the potential of misreading amperages seen with ECM motors caused by
    these harmonics. These effects can be minimized through the installation of a low cost choke on the power
    line.
    The building electrical layout should be designed to accommodate the resultant harmonics, and design
    features such as slightly increased neutral wire size at the electrical panel should be considered

    http://www.krueger-hvac.com/lit/pdf/whiteecm.pdf
    Another good one:http://stevenengineering.com/Tech_Su...PDFs/45FFC.pdf
    Last edited by tipsrfine; 01-20-2010 at 10:46 AM. Reason: add on

  8. #328
    Join Date
    Jul 2007
    Location
    Delta BC Canada
    Posts
    140
    Post Likes

    Power factor choke

    Because it is a multi speed motor and older ,I thinkthe PFC is a coil of wire to just add some inductance to the circuit. The capacitor may be ok for low speed but have some adverse affects on efficency at high speed .

  9. #329
    Join Date
    Nov 2008
    Location
    Meriden, Kansas
    Posts
    435
    Post Likes
    Quote Originally Posted by Pneuma View Post
    Now another question, what harm is being prevented? What would the harmonics do if not prevented/reduced by the choke?
    I really just know enough to be dangerous about power quality, but I have worked through a few issues before in schools and industrial plants.
    I don't know specifically why ECM designers choose to reduce harmonics. Were ECMs causing a problem on the equipment they were used in, or were the designers just being good citizens?
    I do know that non-sinusoidal loads cause harmonics and cause little voltage and amperage spikes which are hard on electronic components, particularly capacitors. The most common problem is on any system with a shared neutral. Even though the average amperage is OK, the amperage on the neutral conductors can exceed the wire rating (overheated neutrals). Also the harmonics at higher frequencies and can be hard on transformers and coils.

  10. #330
    Join Date
    Dec 2009
    Location
    Buffalo, N.Y
    Posts
    101
    Post Likes
    Thread Starter

    A Solution !!!!!!......finally.

    Called back after many months to do a start-up on same unit. Problem is, after many months of customer-electrician power factor pondering, nothing had changed.
    Motor still had same run characteristics on site, but there was a detailed bench test report from a local electric repair shop stating motor was fine. I know the man who performed the benchtest and trust that if he documents specs, they're fact. Report stated 8.9 unloaded amp draw and 10.9 loaded amp draw- both at 230 VAC.
    Customers power supply had been logged and varied from 244 to 253 VAC. I Inquired to customer's electrician if it were possible to reduce applied power for testing. He suggested adding a buck & boost transformer to the motor leads on the load side of the contactor. Transformer installed,220 VAC applied, unloaded motor drew 8.8A, when installed with original sheave amp draw was 9.7A. Simple as that.
    Though earlier in the troubleshooting process I leaned hard on power factor issues, That turned out to be only a symptom of the real problem, poorly designed motor. It appears to me that the motors nameplate voltage of 208/230 doesn't honor the old 10% over rule of thumb.

  11. #331
    Join Date
    Sep 2009
    Location
    Arnold mo
    Posts
    3,974
    Post Likes
    Quote Originally Posted by fruecrue View Post
    Called back after many months to do a start-up on same unit. Problem is, after many months of customer-electrician power factor pondering, nothing had changed.
    Motor still had same run characteristics on site, but there was a detailed bench test report from a local electric repair shop stating motor was fine. I know the man who performed the benchtest and trust that if he documents specs, they're fact. Report stated 8.9 unloaded amp draw and 10.9 loaded amp draw- both at 230 VAC.
    Customers power supply had been logged and varied from 244 to 253 VAC. I Inquired to customer's electrician if it were possible to reduce applied power for testing. He suggested adding a buck & boost transformer to the motor leads on the load side of the contactor. Transformer installed,220 VAC applied, unloaded motor drew 8.8A, when installed with original sheave amp draw was 9.7A. Simple as that.
    Though earlier in the troubleshooting process I leaned hard on power factor issues, That turned out to be only a symptom of the real problem, poorly designed motor. It appears to me that the motors nameplate voltage of 208/230 doesn't honor the old 10% over rule of thumb.
    The prodigal son returns. I thought you had a few different motors from different manufactuers? Doesn't add up all their nameplates are mis-leading. We have to get darth vader back in on this one.

  12. #332
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,346
    Post Likes

    *

    ok, i forgot;

    what was the problem

    what was the cause of the problem

    what was the repair for the problem

    or is the problem still in internet limbo



    .

  13. #333
    Join Date
    Sep 2009
    Location
    Arnold mo
    Posts
    3,974
    Post Likes
    Quote Originally Posted by Airmechanical View Post
    ok, i forgot;

    what was the problem

    what was the cause of the problem

    what was the repair for the problem

    or is the problem still in internet limbo



    .
    The problem was the motor was drawing high amps & burning out. Now he says the problem was the motor was being supplied with too high voltage and that he fixed the problem by reducing the supply voltage.
    I'm hoping that is enough to resurect this thread. Lowering voltage on an induction run motor reduced amps.

  14. #334
    Join Date
    Dec 2009
    Location
    Hotlanta GA.
    Posts
    218
    Post Likes
    Well I'll be dammed, like I said from the start, the framastat was miss adjusted, causing the unballance of the flux capacitor, there by showing an offset in the P= E x I formula !!!

    Good thing I sat back on my bucket and pondered on this one.

  15. #335
    Join Date
    Dec 2009
    Location
    Buffalo, N.Y
    Posts
    101
    Post Likes
    Thread Starter
    Yup, now we have a spare in stock. Both motors (one G.E., one Emerson) were manufactured by the same company in Mexico.

  16. #336
    Join Date
    Oct 2009
    Location
    Finland
    Posts
    135
    Post Likes
    Well, i hope you guys had fun at the convention.
    See page 4.

  17. #337
    Join Date
    Sep 2004
    Posts
    13,938
    Post Likes
    same amp draw with or without belt?????????????
    do you know how to determine brake horsepower??

    that is impossible!!!!!!!!!!!!

    maybe a bad meter????????????????????????????
    true knowledge exists in knowing that you know nothing.

  18. #338
    Join Date
    Sep 2004
    Posts
    13,938
    Post Likes
    ofcourse this is from Norm!

    http://www.bacharach-training.com/norm/electric.htm

    Electric Motor Brake Horsepower Calculations
    By Norm Christopherson


    These motor calculations are contained here as they apply to the changing conditions of the blower motor when pulley adjustments are made. However, these calculations are useful wherever electric motors are used. What is learned here can be used to solve motor installation and troubleshooting problems in a large variety of applications. These motor formulas and related information is also basic to understanding energy consumption, power consumption by motor driven devices and the motor side of performing energy audits.

    Fundamental to these useful calculations is some understanding of the information contained on a motor data plate.



    Motor Data Plate Information Explained


    Every motor has a metal nameplate or data plate listing the manufacturer, motor type and electrical requirements for the motor.



    Voltage
    The voltage listed on the data plate is the design voltage the motor was made for. The motor may be operated at any voltage within 10% of the design voltage.



    Full Load Amps (FLA)

    This amperage is the current the motor will draw when the motor is loaded up to its rated horsepower. The motor will draw less than the listed FLA if the motor is operating at less than the rated horsepower. The motor will draw more than the rated FLA when it attempts to operate at more than the rated horsepower. Measuring the actual motor amperage and comparing it to the FLA is a good way to quickly tell if a motor is overloaded.



    Locked Rotor Amps (LRA)

    This amperage is the current the motor will draw when the motor is started and when the motor is attempting to start and run but is unable to do so for some reason such as mechanically stuck bearings. A rotor is said to be locked anytime the rotor is not rotating. This is normal on a motor that is off and ready to start. If a motor has bad bearings and cannot start, the proper terminology for that condition is to say the motor has stuck or frozen bearings. It would not be correct to say the motor has a locked rotor. All motors when off have locked rotors. The LRA rating of a motor is the most amperage the motor can draw under any condition.



    %Efficiency

    The rated percent of efficiency for the motor is listed on most motors but not all. Motors that fail to state their efficiency probably have poor efficiency ratings. If the efficiency is not given it can still be determined using basic math. This formula is included in this book later in this chapter. Generally higher efficiency motors are those that use more metal in their construction and the metal is laminated and insulated between laminations to reduce eddy currents, which create heat. Heat in a motor is lost efficiency. The efficiency rating may be given as a percent such as 86%, or the same percentage may be listed as a decimal fraction like .86. When using the percent efficiency in a math formula, it must be used as a decimal fraction.



    Power Factor
    The power factor is also given as a decimal fraction and may be any number less than one. Common power factor ratings range from .70 to .98. The higher power factor is always more desirable.

    The power factor is a number, which tells to what extent the motor voltage and current are out of phase from one another. Unlike pure resistive circuits like electric heaters and incandescent lights, motors operate with strong magnetic fields present. The magnetic fields add a new element of magnetic resistance to the motor circuit, which throws the voltage and current out of phase from each other. When the voltage and current are not in phase ohm's law will not work unless the power factor is used to correct for this phase difference. The power factor listed on a motor is very useful to the technician when making motor horsepower and current calculations. These handy calculations are included in this chapter.



    Service Factor
    The service factor of a motor is a number, which indicates how much more work a given motor, can do beyond the rated horsepower. This is a safety factor and is not to be considered as a part of the motors normal useful horsepower. A motor may have no service factor whatsoever and thus has no safety factor in the event the motor becomes overloaded. A common service factor on motors is a SF of 1.15. This number multiplied times the rated horsepower gives the actual horsepower the motor could operate at in an emergency. For example; a 10 HP motor with a SF of 1.15 could actually provide service for a short time up to 11.5 HP. A motor with a high service factor is used on applications where the load may vary and may occasionally be confronted with an unexpected overload in horsepower. Air conditioning systems often use motors with the SF rating of 1.15.

    The service factor can also be multiplied times the FLA of the motor to give the absolute highest operating amperage the motor should be allowed to operate with. This use of the service factor is not recommended, as it is not completely reliable as it assumes the voltage the motor is getting is exactly correct. This is also a poor service practice because it encourages technicians to allow loading motors up into the safety zone the service factor provides.



    Motor Horsepower Calculations
    Some motors such as air conditioning and refrigeration compressors do not state their motor horsepower. A rule of thumb for air conditioning compressor motors is that there is one horsepower per ton. This rule will not work for applications other than comfort cooling air conditioning applications. The number of horsepower required to provide each ton of cooling varies with the suction pressure and head pressure. The higher the head pressure or the lower the suction pressures, the more motor horsepower required to achieve a ton of cooling. Another way of stating it is that as the pressure difference between the suction and head pressures increase, the system tonnage decreases. This is why it is so important to keep condensers clean, evaporator air filters replaced and airflow on both condensers and evaporators up to normal. Anything, which increases head pressure or decreases suction pressure will decrease system capacity and at the same time increase operating costs.

    The ability to determine actual motor operating horsepower on any motor, compressor motor, evaporator blower motor or tower motor, is useful in troubleshooting problems or performing energy audits. Understanding the elements and process of basic motor horsepower calculations also increases awareness of energy consumption, motor operation and potential problem areas.







    The formula given above is used to determine the actual operating horsepower of any single-phase motor. If a motor such as a compressor does not state the motor horsepower, then this formula will also work to determine the rated or actual operating horsepower.

    If the motor name/data plate information such as the rated voltage, rated fla, rated efficiency and listed power factor are placed in the formula, the resulting answer will be the rated horsepower. Of course there is not reason to use the formula in that way unless the motor is a compressor and does not state the motor horsepower.

    The common use for this calculation is to determine the actual operating horsepower for a motor as it is presently being used. If a blower motor for example, is going to get a drive pulley change this formula will give the motors actual operating horsepower prior to the change so the technician can tell if the motor has enough horsepower capacity available or if the motor must be changed. If the motor must be changed this calculation also gives added information to help determine what new size motor will be necessary when the pulley is changed.



    Example:



    A single-phase blower motor has the following data plate information.



    5 HP 230 Volts FLA 20.72

    %Eff .86 PF .91 SF 1.15



    A technician measures the actual running amperage and voltage and finds the motor is getting 230 volts and is drawing 16 amps. The amperage is less than full load so the motor is not working at the 5 HP it is rated for. But, what amount of work is it actually doing? Inserting actual measured values of voltage and amperage in the formula gives the answer.



















    The calculation shows the motor to be operating about one horsepower under the 5HP rating.

    A careful look at the single-phase horsepower formula reveals some useful information. The power law states that the voltage (E) times the amperage (I) gives the wattage or power consumption of a circuit. Therefore the horsepower formula includes both voltage and amperage. There are 746 watts in one horsepower, so every time a motor develops or uses 746 watts it has done one horsepower of work. Both wattage and horsepower are two ways of stating the same thing. This is why the 746 watts per horsepower is divided into the watts on the top of the formula.

    But, notice that the voltage times the amperage in the top of the formula not only gives the wattage but the wattage is then multiplied times the % efficiency and the power factor. The wattage gotten by multiplying the motor voltage times the motor amperage assumes that the motor is 100% efficient. Nothing is 100% efficient and motors are no exception. The efficiency of this motor is 86 % so; the wattage is reduced to 86 % of the calculated wattage by multiplying by .86. The lost efficiency was lost in the form of heat and never produced the work in the form of rotational force which motors are made to do.

    Obviously the higher the efficiency the better and also the higher the initial cost to purchase. However, the energy savings from the higher efficiency may offset the higher initial cost. Remember, the power the power bill reflects is all the power the motor uses, not just what the motor converted to useful rotational work but even the power lost to heat. A higher efficiency motor wastes less power to heat loss and may run less to get the same amount of work accomplished than a lower efficiency motor. Generally, it pays to purchase higher efficiency motors to begin with unless the motor is a small one. Small motors usually do not consume enough power to pay back the cost of the higher efficiency.

    After correcting the motor wattage for the efficiency of the motor, the result is then corrected for the power factor of the motor by multiplying by the power factor rating listed on the motor data plate. The power factor was defined earlier in the chapter as the degree that the voltage and current are out of phase from one another. A power factor less than one indicates that the two are not perfectly in phase so the actual power the motor is working at is not what it could be if the voltage and amperage were perfectly in phase. Knowing and using the power factor and efficiency in motor calculations is vitally important if solid useful numbers are to be gotten.













    The calculation shows the motor to be operating about one horsepower under the 5HP rating.

    A careful look at the single-phase horsepower formula reveals some useful information. The power law states that the voltage (E) times the amperage (I) gives the wattage or power consumption of a circuit. Therefore the horsepower formula includes both voltage and amperage. There are 746 watts in one horsepower, so every time a motor develops or uses 746 watts it has done one horsepower of work. Both wattage and horsepower are two ways of stating the same thing. This is why the 746 watts per horsepower is divided into the watts on the top of the formula.

    But, notice that the voltage times the amperage in the top of the formula not only gives the wattage but the wattage is then multiplied times the % efficiency and the power factor. The wattage gotten by multiplying the motor voltage times the motor amperage assumes that the motor is 100% efficient. Nothing is 100% efficient and motors are no exception. The efficiency of this motor is 86 % so; the wattage is reduced to 86 % of the calculated wattage by multiplying by .86. The lost efficiency was lost in the form of heat and never produced the work in the form of rotational force which motors are made to do.

    Obviously the higher the efficiency the better and also the higher the initial cost to purchase. However, the energy savings from the higher efficiency may offset the higher initial cost. Remember, the power the power bill reflects is all the power the motor uses, not just what the motor converted to useful rotational work but even the power lost to heat. A higher efficiency motor wastes less power to heat loss and may run less to get the same amount of work accomplished than a lower efficiency motor. Generally, it pays to purchase higher efficiency motors to begin with unless the motor is a small one. Small motors usually do not consume enough power to pay back the cost of the higher efficiency.

    After correcting the motor wattage for the efficiency of the motor, the result is then corrected for the power factor of the motor by multiplying by the power factor rating listed on the motor data plate. The power factor was defined earlier in the chapter as the degree that the voltage and current are out of phase from one another. A power factor less than one indicates that the two are not perfectly in phase so the actual power the motor is working at is not what it could be if the voltage and amperage were perfectly in phase. Knowing and using the power factor and efficiency in motor calculations is vitally important if solid useful numbers are desired.



    Three Phase HP Calculations
    Three phase motors use the same calculation as was used on single-phase motors with one addition to the formula. Three phase motors have three separate voltages each 120 degrees out of phase from on another. This is what gives the three phase motor its superior starting and running power and eliminates the need for start capacitors and start relays to remove a starting winding as is often necessary on single phase motors.

    The three-phase motor is 73% more powerful than an equivalent motor using single phase. The number 1.73 is added to the wattage side of the calculation to reflect this increase for 3 phases.



    Here is the three-phase formula for determining motor horsepower including the addition of the 1.73 in its proper place. The 1.73 is the square root of the number 3 for the 3 phases.

    In order to determine missing values of efficiency and/or power factor the formula is the same as for single phase except the 1.73 is included in the calculation.





    Use this formula just like the single-phase version.



    RELATIONSHIPS BETWEEN RPM, CFM, PULLEY DIA, HORSEPOWER AND MOTOR AMPS.
    The technician who works with blowers and blower motors and makes adjustments to correct airflow quantities must understand the relationships between the various elements involved. A change in any one of the operating conditions will have an important effect on several others. Making adjustments without considering the effects of the adjustments may cause a blower motor burnout or may result in an inefficient system operation. The purpose of making adjustments in the first place is to increase efficiency and provide for increased comfort at lowered operating costs as well as to avoid causing expensive system failures.



    Relationship of Rpm to Cfm.

    To increase cfm the blower rpm must be increased. This is a directly proportional change. The percent of cfm change is proportional to the percent of rpm change. Since the rpm and cfm are directly proportional, the two are interchangeable in formulas. Where one is used the other may be substituted.



    Relationship of Rpm and Cfm to the Motor Pulley Size.

    To increase the rpm and cfm of the blower the motor pulley size must be increased. This relationship is easy to remember as the motor pulley is always smaller than the blower pulley and if the motor pulley were made the same size as the larger blower pulley they would both go the same speed, which is the speed of the motor. Except for direct drive, no blower operates at the same speed as the motor.

    The relationship of the rpm, cfm, and motor pulley is a directly proportional one. The rpm and cfm change by the same percentage change of the motor pulley change.



    This paper was taken from a larger work by the same author. The full text of the larger work goes into greater depth, detail and provides additional material.

    Norm is a technical writer, seminar speaker and test proctor for EPA, 410A and ESCO & NATE certifications.

    He can be contacted at nchristo@juno.com
    true knowledge exists in knowing that you know nothing.

  19. #339
    Join Date
    Sep 2004
    Posts
    13,938
    Post Likes
    if you look at the performance curve of any induction motor?
    you will see, 10% under draws more amps! up to 10% over draws less amps, more than 10 over draws more amps!!
    too bad it is not as simple as volts times amps! all that stupidmagnetic flux, impedence, inductance,reactive power, real power and apparent power!!!


    Quote Originally Posted by tipsrfine View Post
    The problem was the motor was drawing high amps & burning out. Now he says the problem was the motor was being supplied with too high voltage and that he fixed the problem by reducing the supply voltage.
    I'm hoping that is enough to resurect this thread. Lowering voltage on an induction run motor reduced amps.
    true knowledge exists in knowing that you know nothing.

  20. #340
    Join Date
    May 2007
    Location
    Dry as a bone Tucson
    Posts
    4,866
    Post Likes
    [quote=supertek65;6688452]same amp draw with or without belt?????????????
    do you know how to determine brake horsepower??

    that is impossible!!!!!!!!!!!!

    maybe a bad meter????????????????????????????
    his batteries were low,
    "I aint going to spit on 30 years of my life" Monte Walsh


Page 17 of 19 FirstFirst ... 710111213141516171819 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •