    Confused out of ideas
    I have a 2 hp squirrel cage blower kicking my ass. after about 200 hours run time max, motor #1 failed, overload stopped resetting. motor was drawing @ 10 amps, nameplate 11. Motor #2, drawing just under 11 amps, same sheave, same motor. #2 started cycling on overload after two weeks. when I was called, it was drawing 12.6 amps, cycling on OL, windings were chocolate color, checked capacitors, bought smaller sheave, motor draws 12.6 amps even unloaded. Replaced run cap., 12.6 amps. 4.15" sheave or 3.25" full open, 12.6 amps. WTF. Ok, motor is toast, got a new one,put it in.
    New motor runs the same, 12.6 amps. Motors all the same- 208/230 single phase. Line voltage is 246.5 with unit off, 244.9 running. Block the return air with cardboard- 12.6 amps. run without belt, 12.6 A. 4.15" sheave, motor loaded as much as I can, 12.6 amps. 3.25" sheave, 12.6 A
    UGGGHHHH.
    Customer has a newbuild 15,000 square foot home with all low voltage lighting. I start trying to shed power to the lights to see if anything changes. My thought was that all those electronics may be somehow altering frequency or changing the incoming power . No help, 12.6 A. This is one of my two residential accounts but all the equipment is commercial. I started questioning the 246.5 applied voltage, but it is within 10% of nameplate. measured 60 hertz, with lighting energized and off.
    I am out of options. right now my plan is to take both motors (#2 and #3) to be bench tested at a local electric repair shop.
    Any ideas or suggestions would be appreciated. If you made it this far into my long post, thanks.
    Dave.
    East of big city prices.
    What kind of equipment is it? If it's a air handler how much air is it moving? Is it TEFC ? I'll think of more later.
    Dec 2009
    Buffalo, N.Y
    Quote Originally Posted by thegoodlistener View Post
    Its a geo-thermal pool unit with de-hum, re-heat, waste heat recovery, the whole nine. I have not measured airflow. The arrogant engineer designed this system at 3200 cfm (8 ton) and claims to have done such a perfect job that no balancing dampers are necessary. I did not install the ductwork, nor did my company have anything to do with it. I simply set up the blower by amp draw.I am trying to Isolate just this component to simplify things.
    TEFC? I'm drawing a blank on that one.
    Other details I forgot to mention, I am able to run only the blower, through its contactor and nothing else but wires, all thoroughly checked for any defect.
    Totally
    enclosed
    fan
    cooled motor
    Dec 2009
    Buffalo, N.Y
    Totally
    enclosed
    fan
    cooled motor
    No, open.
    Well, since it is a squirrel cage, we rule out an air restriction which would actually reduce amperage.
    Honestly, since you say that the new motor was over amping, too, I have to vote for a mis-match. Call the manufacturer and verify that all components are correct for the application.
    Dec 2009
    Buffalo, N.Y
    manufacturer has supplied all motors. I toyed with the idea that 2 hp wasn't enough, but I can't even spin the blower, without moving air, at less than 12.6 A. Even without the belt, a motor is a motor, regardless of size, I would expect 5/8 to 3/4 fla.
    thanks for the replies.
    Jul 2009
    In a mechanical room....
    Is the home supplied with 3 phase and your taping a single phase off of that?
    Current Harmonics, and phase imbalance can occur on single phase equipment if i'm not mistaken. Are the start windings not DE energizing after motor spins up?
    Reliable, long-term operation of most electrical equipment requires a voltage imbalance of less than two percent; which means your system has too much imbalance.
    If you find voltage imbalances in your facility, the first place to look is not the power company. Instead, look for electrical distribution systems in which one leg of a 3-phase supply powers both single-phase and 3-phase loads. You may find single phase loads not evenly balanced across the phases. Or, look for in-line reactors installed to correct imbalances. These reactors usually have taps for adjustment, and somebody may have adjusted them. Or, the imbalance they originally corrected may have shifted over time. Circuits with tapped reactors rarely stay in balance indefinitely.
    Now, here's a practice question. You go out onto the floor and find a 460V motor with phase voltages of 458V, 465V, and 480V. Is there a problem or not? There sure is.
    Lowest voltage is 458V. First, calculate your four percent. 0.042458V 418.32V. The difference between the highest voltage (480V) and the lowest voltage (458V) is 22V (480-458). Since the difference (22V) is greater than 4% of the lowest voltage (18.32V), the phases are too far out of balance to ensure continued, reliable operation of electrical equipment.
    Dec 2009
    Buffalo, N.Y
    So, the motor is drawing over FLA without a belt on it?
    yup- 11 A FLA, 12.6 A measured, two different motors, two different meters.
    Dec 2009
    Ontario , Canada .
    Quote Originally Posted by fruecrue View Post
    If it is possible , it would be very interesting to see the performance characteristics of the motor or motors at your local motor repair shop . Provide them with all the information you have , and let them test the motors on the bench . If everything checks out , ie. not drawing FLA with NO LOAD , then you will be getting warmer to the solution . Worst case scenario , they should be able to provide you with more information as to what your problem is and maybe provide some testing equipment to help you . If the cant they will know someone who can .
    Peace
    Dec 2009
    Buffalo, N.Y
    Thumbs up
    Quote Originally Posted by CumulusMech View Post
    Peace
    Well said, thanks.
    is motor multi-voltage?
    when you get the next motor.........ohm it out
    have mfg give you the spec resistance of windings