Results 53 to 59 of 59
06-07-2012, 12:48 AM #53
lol...you must work for or rep a geo company.
The addition of a condenser fan does not make a AC unit low effeciency. Plenty of high seer air source units that are far cheaper to install and much more practical in some parts of the Country.
It reminds me of the guys that push heat pumps in my neck of the woods when natuaral gas is practically given away.
08-27-2012, 10:34 AM #54
New Guest
- Aug 2012
- Upstate NY
- 3
Old post but I thought I'd put some numbers to the question....
Assume the hp is rejecting 3 tons of heat into a medium sized inground pool of 20,000 gallons.
Heat into pool 36,000 btu/hr
Specific heat of water 1 Btu/lbm-°F
Pool water volume 20,000 gal (167,000 lbs)
=167,000 lbs / (36,000 btu/hr / 1 Btu/lbm-°F)
=4.63 hrs/°F
So for about every 4.6 hrs of run time on the heat pump, the pool water temp would increase 1 degree.
This is assuming no other heat transfer to the air/ground/eveaporation/solar which there obviously will be. During the summer months I think it is safe to say that the pool temp would hit the 100F mark without much trouble after a couple of weeks. I live in upstate NY and even without the solar cover my inground pool maintains 80F+ during july and august (especially this summer). From a more practicle point of view, any pool warmer than 85 starts to feel like bathwater to me.
08-27-2012, 12:01 PM #55
The whole concept is reffered to as a " geo battery " and all the math I have seen on operateing it, the pool/or burried tank is allways followed by how much btu replenishment of the battery in fresh water in and hot or cold water is needed opposed to hours of operation for the heat pump. The one that was built and works was a coil of copper pipe put into a tank that was fed continuously by a natural spring at a slow rate and then piped to waste in the nearby creek. It enjoys being a closed, open loop/ with continuous replenishment. I think the load was around 3 tons or so.
Eric
08-27-2012, 04:05 PM #56
But it won't evaporation is pretty significant and the warmer the water is, the higher the evaporation rate. Plus it will reject more heat into the ground as well. But yes, it would raise the pool temp. 5-7F wouldn't suprise me. I don't think that's enough heat to hold much over 90F. But it might make the pool less enjoyable mid-summer.
08-27-2012, 06:05 PM #57
- Jun 2012
- Louisville, KY
- 141
To OP - Not to over-simplify, but wouldn't it cheaper and simpler - if you are just trying to cool a relatively small space for a couple hours at a time - to install a small ductless AC or, heck, even window units? I'm not a tech but this whole pool setup seems like overkill!!
09-19-2012, 09:45 PM #58
New Guest
- Sep 2012
- 1
Waste Heat From House To Swimming Pool
I built a system such as the one that is in question here and it is in its sixth year of operation. The WSHP is a Climate Master 5 ton that was designed/intended for geothermal application. The only water the WSHP has ever seen is the water from a 18x36x6 vinyl ig pool, location being Long Island,NY.
I am a professional pool builder by trade, not HVAC. The system works flawlessly and is part of a pool system that creates more energy than it consumes. ( No this is not over-unity nonsense), but relies on the fact that the pool is idle for 5 months of the year.
Should anyone need free advice on how to heat your pool for free, do not hesitate to contact me.
11-07-2012, 10:04 PM #59
- Jun 2011
- Virginia Beach VA
- 28
Actually, a 36000 BTU unit will have to reject at least 15000BTU per ton or total 45000BTU/h for 3 tons including superheat etc. So in a 8 hour day of running AC you would get somewhere around 360,000BTU, which is equal to about 7 of the extra large solar water heating panels from somewhere like aquatherm. That's enough to maintain heat in most pools. There are some products on the market that heat pools with air conditioners, not sure if they work with heat pumps. Google hotspot pool heater to see an example.